Dell C5000 with C5220 blades

We are running several C5000 with C5220 blades in our data centers.  We ran into an issue.  I am sure there is a solution, but I just have not figured it out.  Any help would be much appreciated!  Thank you.

 

1) IPMI web page goes down, but the IPMI IP still pings. It doesn't even make sense. They go down after a few days to a week.  Someone has to go into the data center and pull the blade out and put it back in.  We keep re-seating the blades, only for the issues to re-appear. We thought an update of the BIOS and IPMI would help, but it didn’t.

 

Has anyone seen this before?  Would love to solve this issue.

 

Thank you.

Reply
6 Replies
Moderator
Moderator

Re: Dell C5000 with C5220 blades

TheServerNinja,

 

Would you confirm a couple things for me please?
What OS installed on the systems?
How are you connected, are you using the individual sled nics or the chassis connection? I ask as using both to connect to the servers or their BMC's can cause packet collisions (causing disruption in nic connectivity)
When updating, did you also include the BMC update?

Lastly, do you see anything in the logs near the time it fails?

Let me know what you see.



Chris Hawk

Dell | Social Outreach Services - Enterprise
Get Support on Twitter @DellCaresPro 
Download the Dell Quick Resource Locator app today to access PowerEdge support content on your mobile device! (iOS, Android, Windows)

Reply
Highlighted
TheServerNinja
2 Bronze

Re: Dell C5000 with C5220 blades

Thank you for you help Chris.  Very much appreciated.

 

What OS installed on the systems?

 

A: It's a mix of CentOS, ubuntu, windows, etc. Even when the blades haven't been used yet with no OS or drive, it still loses connection to the GUI page after a few days to a week max.

 

 

How are you connected, are you using the individual sled nics or the chassis connection? I ask as using both to connect to the servers or their BMC's can cause packet collisions (causing disruption in nic connectivity)



A: Individual sled NICS. All blades have 2 LAN connections. Our chassis's are the one single port chassis for BMC and these chassis's do not have dedicated BMC/IPMI ports... Our only option is to use the single BMC port that is located by the power cords. But yes this makes the most sense on why they would be going down.  Is there a solution?




When updating, did you also include the BMC update?

 

A: BMC and BIOS have already been updated to the latest version on ALL of them.

 

Lastly, do you see anything in the logs near the time it fails?

 

A: No log

Reply
Highlighted
TheServerNinja
2 Bronze

Re: Dell C5000 with C5220 blades

Hi Chris,

 

Hope you had a nice weekend.

 

Please let us know if you have any solutions to this issue.

 

Thank you.  Have a good one.

 

Ninjas

Reply
Highlighted
Moderator
Moderator

Re: Dell C5000 with C5220 blades

So is this what you're seeing?

 

8_sled_front.jpg

 

 

Chris Hawk

Dell | Social Outreach Services - Enterprise
Get Support on Twitter @DellCaresPro 
Download the Dell Quick Resource Locator app today to access PowerEdge support content on your mobile device! (iOS, Android, Windows)

Reply
Highlighted
TheServerNinja
2 Bronze

Re: Dell C5000 with C5220 blades

Hi Chris,

 

Thanks again for the support.

 

1,2,4 and 5 are all correct.  3 is not since we have 12 nodes in our chassis.

 

Thank you

 

Ninjas

Reply
Highlighted
Moderator
Moderator

Re: Dell C5000 with C5220 blades


The BMC is configured in each individual server sled BIOS. The Default NIC setting is "Dedicated", which means all sleds are accessed through the single BMC port (located as you stated near the power cords). Once the BIOS BMC IP Address information has been configured on each of the installed sleds, BMC Management must be done EITHER through the Dedicated single dedicated BMC port for all sleds, OR through the Shared LOM 1 port specified on each additional sled front.

So you would need to either have them all accessible through the BMC port, or individually accessible through there individual NIC ports, but if you chose this you would have to remove the cable from the BMC port.

 

Chris Hawk

Dell | Social Outreach Services - Enterprise
Get Support on Twitter @DellCaresPro 
Download the Dell Quick Resource Locator app today to access PowerEdge support content on your mobile device! (iOS, Android, Windows)

Reply