Hi All,
I have been digging around trying to figure if our little CX3-20 can integrate with our APC ISX manager, in particular power chute network shutdown. Would I be right in saying that there is no out of the box solution to do this?
If not is there away to pass a SNMP trap to the SP's to start a shutdown?
I understand that there is a risk that the trap may arrive prior to all of the hosts shutting down. Already been through that with a Fast-T.
Regards
John
I have been digging around trying to figure if our little CX3-20 can integrate with our APC ISX manager, in particular power chute network shutdown. Would I be right in saying that there is no out of the box solution to do this?
If not is there away to pass a SNMP trap to the SP's to start a shutdown?
I understand that there is a risk that the trap may arrive prior to all of the hosts shutting down. Already been through that with a Fast-T.
Regards
John
wescott1
36 Posts
1
October 22nd, 2008 08:00
The SP's do not respond to SNMP traps.
Loudenj
45 Posts
0
October 22nd, 2008 13:00
Thanks for your reply. One question though, if the shutdown command has been given, does this imply the cache has been flushed and anything has been committed sucessfully? If so then at that stage I'm not to concerned about power draw as the CX should the be last thing still running.
Cheers John
wescott1
36 Posts
0
October 23rd, 2008 07:00
imply the cache has been flushed and anything has
been committed sucessfully?
The shutdown commands are, I think, supported only on
CX4 and AX4 at this time.
All data on the array will be saved with shutdown, but the
attached hosts need to be stopped first.
draw as the CX should the be last thing still running.
Then why shut the array down at all? Just power down the
attached hosts. The array will then gracefully handle loss of power
when it happens.