Storage Array Faulted Bus 0 Enclosure 0 : Faulted after SPS Test

Our new manager finds the aforementioned weekly error message annoying.

Just wonder whether there is any harm to disable the Event 2580 Error from the template ?  Do we need Engineering Mode to do so ?

Thanks

Labels (1)
0 Kudos
2 Replies
Highlighted
3 Argentum

Re: Storage Array Faulted Bus 0 Enclosure 0 : Faulted after SPS Test

Hi Tony,

The event number 2580 should be unchecked in the monitor template. According to EMC Engineering, event 2580 event is always called during an SPS test even if the SPS has no problems. That is why this event is not monitored. If there is a problem with the SPS, a subsequent event will identify the problem and dial home.

Note: Navisphere may need to be in engineering mode in order to access the template properties.

For more information please refer EMC KB article 45307.

Thanks

Jyothi

Highlighted
3 Zinc

Re: Storage Array Faulted Bus 0 Enclosure 0 : Faulted after SPS Test

Hi,

Since we are using the same template for both CX4-120 and VNX5100 SAN, would it be a problem for VNX SAN if we unselect the Event Number 2580 ?

Thanks

0 Kudos