Boost Mode on a Dell UPS 1920W

Hello,

I have upgraded my DELL UPS 1920W to the last firmware, 01.14.0003 and I am using the last Local Node Manager. 

In the evenement log, I see a lot of Entering Boost Mode records and also returning to normal mode 

Is it normal ? 

what doest it mean ? 

I include some records of the log file

"Date","Nœud","Type","Niveau","Objet","Valeur","Message"
"2014/02/09-17:37:58.595","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-16:30:54.905","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-16:16:54.150","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-16:10:53.873","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-16:08:53.841","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-15:52:52.915","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-15:41:52.135","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-15:37:52.005","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-15:36:51.985","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-15:29:51.704","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-15:28:51.674","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-15:09:50.110","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-14:53:48.687","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-14:52:48.576","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-14:43:47.647","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-12:36:40.789","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-12:35:40.769","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-12:22:40.258","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-12:19:39.877","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-12:16:39.747","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-12:01:38.645","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-11:36:37.323","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-11:35:37.277","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-11:34:37.211","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-11:27:36.918","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-11:15:35.963","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-11:13:35.931","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-11:12:35.905","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-11:10:35.803","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-10:25:33.125","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-10:24:33.089","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-10:23:33.053","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-10:22:33.047","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-09:27:30.044","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-09:25:29.894","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-06:42:20.552","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-06:41:20.532","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-06:10:18.256","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-06:09:18.236","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-06:04:17.614","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-05:55:16.612","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-05:46:16.292","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-05:40:16.015","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-04:51:12.732","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-04:50:12.696","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-04:38:11.624","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-04:37:11.277","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-04:36:11.251","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/09-04:34:11.169","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/09-04:29:10.968","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-23:02:52.268","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-22:43:50.922","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-22:38:50.752","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-20:55:44.307","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-20:54:44.287","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-18:54:36.653","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-18:53:36.337","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-18:52:36.320","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-18:45:35.949","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-18:43:35.879","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-18:40:35.748","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-18:24:35.024","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-18:12:34.161","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-18:08:34.061","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-18:06:33.881","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-18:02:33.770","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"
"2014/02/08-17:59:33.460","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","2","UPS.PowerConverter.Input[1].PresentStatus.Boost","1","Mode boost"
"2014/02/08-17:56:33.339","Dell UPS Tower 1920W HV UPS LI T 1920","Evènement","1","UPS.PowerConverter.Input[1].PresentStatus.Boost","0","Retour du mode boost en mode normal"

Tags (1)
0 Kudos
12 Replies

RE: Boost Mode on a Dell UPS 1920W

Boost mode means the UPS is taking the input voltage and boosting it to the correct output voltage without having to have the UPS go on battery. If this is happening often then either the UPS is set to the wrong output voltage (set to 240 when input is really 220) or there is an actual issue with the input voltage to the UPS. Having the UPS operate in boost mode does not effect reliability.

0 Kudos
yves67
Bronze

RE: Boost Mode on a Dell UPS 1920W

Hello

I still have boost mode alerts, and checking the ouptut voltage, it is set at 230V

but the input voltage is around 208/210V

I would like to set the output voltage to 220V (to avoid all hte boost mode alerts) but from the panel I cannot change the output value

and in the local node management software, there is no possibility to change the output value

question: is it possible to change the output voltage value ? if yes How ? 

thanks for any help

regards

yves

0 Kudos

RE: Boost Mode on a Dell UPS 1920W

To change the input voltage of the UPS it has to be in the Standby mode (AC still connected to the input but the outputs off). Once you are in Standby mode you can go through the LCD menu of the UPS to change the output voltage. You cannot change the output voltage while the UPS is running (outputs on).

0 Kudos
yves67
Bronze

RE: Boost Mode on a Dell UPS 1920W

Thanks a lot for your answer

I will try it as son as I can shutdown the server 

BTW : do you know where I can find the last version of the firmware for the UPS 1920W ?

Thanks again

Yves67

0 Kudos

RE: Boost Mode on a Dell UPS 1920W

Here is the general landing page for the 1920W UPS

www.dell.com/.../drivers

 

The latest firmware is there as well the firmware upgrade tool. The latest ULNM management tool is also there.

0 Kudos
yves67
Bronze

RE: Boost Mode on a Dell UPS 1920W

OK, Thanks

but the UPS 1920T is equal to the UPS 1920W ??

I have an UPS 1920W

Yves67

0 Kudos

RE: Boost Mode on a Dell UPS 1920W

1920T = 1920W Tower

1920R = 1920W Rack

0 Kudos
yves67
Bronze

RE: Boost Mode on a Dell UPS 1920W

OK, it is the same...

I can go

THANKS for your help

Regards

Yves67

0 Kudos
yves67
Bronze

RE: Boost Mode on a Dell UPS 1920W

Hello,

Last week end I could shut down the server, and I disconnect all the outlets on the UPS 1920W

I tried to change the output voltage, but no way, I cannot change it ???? 

Is there an method to be in stanby mode ? 

I thought with no charge at all I could change the output voltage, but may be I was not in stanby mode ?? 

Thanks for your help

best regards

Yves67

0 Kudos