6021
fx2
has anyone tried to upgrade their power supplies from 120V 1600W to 2000W in order to have full redundancy? we tried upgrading to 2000W but the server won't boot when configured with grid redundancy.
DELL-Daniel My
Moderator
Moderator
•
6.2K Posts
0
December 13th, 2017 11:00
Hello
Did you swap both power supplies to 2000w, and are they receiving the same input voltage? Both PSUs must have the same maximum power output to operate in a redundant configuration. The input voltage will change the power output.
Thanks
bagek
21 Posts
0
December 15th, 2017 08:00
yes we swapped both. is there a specific configuration for redundancy? if we try grid redundancy the server won't boot.
DELL-Daniel My
Moderator
Moderator
•
6.2K Posts
0
December 15th, 2017 09:00
The server functions in a 2+0 configuration but not a 1+1?
Did you change anything else when you upgraded from 1600w PSUs? Were you having any issues with 1600w PSUs?
If you added hardware and it is only working in a 2+0 configuration then you are likely drawing more power than the PSUs are outputting. The PSUs only output around half of their rated wattage on a 120v power connection, so upgrading from a 1600w PSU to a 2000w PSU is only a 200w increase in available power.
Thanks
bagek
21 Posts
0
December 20th, 2017 13:00
can you explain 2+0 and 1+1?
we didn't change anything else. we have only 2 sleds in this unit. we thought changing to the 2000W supplies would give us full redundancy similar to a typical r730 which we use now. is that possible?
thanks for your help
DELL-Daniel My
Moderator
Moderator
•
6.2K Posts
0
December 20th, 2017 14:00
Redundancy policies are explained starting on page 132 of the CMC version 2.0 FX2 manual:
www.dell.com/support/home/product-support/product/poweredge-fx2/
The enclosure manual has information about the expected wattage of the power supply units based on the input voltage.
If you have two of the same PSUs that are connected to the same input voltage then you should be able to run them in a redundant/1+1 configuration. If you are only able to power on the nodes when the PSUs are in a non-redundant/2+0 configuration then the nodes require more power than a single PSU can supply. You will need to use 240v input to increase the available power to the nodes.
Thanks
bagek
21 Posts
0
December 21st, 2017 09:00
. if this is the case it looks like Dell does not have a solution for 1+1 for these 120V servers. we were planning to purchase and deploy more of these but our computer rooms are already built out for 120V and it's cost prohibitive to convert toe 220V now. we only have 2 sleds in these which I would think 1 psu could handle that.
thanks for the update.
ASancho
1 Message
0
July 5th, 2018 02:00
Hi Bagek and Daniel,
Not sure if I have understood completely this conversation. Apparently resolution is that, even changing to 120Vac-2000 Watts power supply, FX2 is not able to run in 1+1 redundancy. Not able to support a single failure upon failure of PS or voltage feed. Correct?
Is it any solution to be given on the future for 120Vac market from Dell?
Thanks and best regards,
Alfonso
BriFar
29 Posts
0
July 9th, 2018 08:00
Hi Alfonso,
Depends on the load.
I don't know if this helps but the FX2 manual , pages 12 and 90, indicates the maximum power available when using the power supplies on low line (120v)
https://topics-cdn.dell.com/pdf/poweredge-fx2_Owners-Manual2_en-us.pdf
You might be better off swapping for the 1100W(1050W low line) or 2400W (1400W low line) PSUs