Start a Conversation

Solved!

Go to Solution

1 Rookie

 • 

2 Posts

23

April 15th, 2024 09:33

120V DC input for 80Plus Platinum powersupply.

The powersupply is mentioned with 100-240V 50/60Hz for AC input OR 240V for DC input.

This means we can connect 110V AC or 230V AC.

However for DC is it only 240V DC, can't we use 120V DC ??

Why the range of DC is not mentioned as like in AC.

Moderator

 • 

3.4K Posts

April 15th, 2024 20:40

Hello,

 

You will need 240V DC input.

 

The PSU label shows:

the A/C says 800W at 100-240V input (gives range)

the DC shows 800W at 240V input (no range )

 

4 Operator

 • 

227 Posts

April 15th, 2024 10:35

Are you looking for DC power for this server? They connect to the server end is the same, but connect to the power cord this end is different!

1 Rookie

 • 

2 Posts

April 15th, 2024 16:18

@hnyr28​ Thanks for detail. The 1100W is not sutiable for me because the input powersupply in 120V DC. This is more that the limit. We like to get confirm that is it allowed to connect 120V DC where the "240V DC autorangeing" is mentioned datasheet. 

No Events found!

Top