CX4-960 Circuit Requirements
I'm planning a DC to one day support a CX4-960 in a specific grid of our DC. Based on my readings, I should plan on having 2 x 20A circuits providng power to support the SPS and SPS and 8 DAEs. Can someone agree or disagree here?
No Events found!


DGM3
238 Posts
0
December 17th, 2008 13:00
That said, some considerations;
- Any other devices that may be co-located with the CX4-960 (e.g. switches) would add to the power draw, which will likely put the config above 16A.
- Any future DAE adds would add to the power drive, which will likely put the config above 16A.
- If the config will be housed in an EMC rack; the EMC racks for CX4-series are configured with L6-30P plugs, which are for 30A service. Also, the PDUs within the EMC rack have breaker protection based on 30A service. Thus if using an EMC rack, you'd want to target 30A service rather than 20A service.
In light of those considerations; using 20A service looks viable if the config will be housed in a non-EMC rack, there are no additional devices drawing power, and no near-term plan to add additional DAEs. Else, 30A service should probably be considered.
Regards,
DGM