UPS Question for an expert

Grandson recently purchased a Windows 10 water-cooled (non-Dell) gaming machine. The PSU is an 850 Watt EVGA SuperNova G2 (AVR). I believe system is overclocked at 4.2-4.8 with 3 GPUs. The monitor is a 4k-compatible unit. Let's say 200 watts.

Fact: Your stated UPS's wattage should always be more than the maximum of tower and peripherals.Schneider, who sells APC, says you should not push UPS past 80% of its stated wattage.

From all that my takeaway is that the required UPS to safely and effectively back up this system would require a minimum of 1200 watts/2000VA.

Appreciate some clarification and suggestions.

PS  Is an under-powered UPS better than no UPS at all or can it potentially cause big problems (specifically to expensive tower).

9 Legend

 • 

47K Posts

November 7th, 2016 07:00

https://www.amazon.com/Tripp-Lite-Line-Interactive-Rackmount-SMC15002URM/dp/B00YXW6MFI/

 

The difference is cost.  15 Amps 120v = 1800W which is 3000VA

Done making suggestions.

 

https://www.tripplite.com/smartpro-lcd-120v-1500va-900w-line-interactive-ups-avr-tower-lcd-usb-10-outlets~SMART1500LCDT/

No idea what PMW is.    Pulse-width modulation (PWM

 

 

4 Operator

 • 

2.3K Posts

November 2nd, 2016 18:00

So i'm not an expert but I have played with UPS systems before and I would say 1000w is big enough.  You should also figure that your grandson will most likely never use all 850 watts of power the PSU outputs even with 3 graphics cards etc.  A UPS system for home is designed only to give you enough time to shut the computer down.  If you are lucky you can finish what your doing (under 3 min) and shut down, but in no way is it designed to continue gaming or doing whatever until the power comes back on.  It does work effectively against spikes and surges.  Someone may chime in with a more detailed explanation as well.

7 Technologist

 • 

7.1K Posts

November 3rd, 2016 04:00

Hi Maxd,

Dell would not recommend you to go for a 1000 watts lower UPS as the system if used with high usage application then the wattage will shoot up to 850 watts.

I would suggest you to purchase the 1.2KV UPS.

9 Legend

 • 

47K Posts

November 3rd, 2016 05:00

The Area 51 with 3 way SLI has 1500W power supply.  I always spec an UPS based on the Circuit its used on.  Typical house outlets are 10 to 15 AMPS max.  

watts = 1 × 15A × 120V = 1800W

80 percent efficient power supply means

watts = 0.8 × 15A × 120V = 1440W

That means if I had an Area 51 and 3 monitors I would get a 30 Amp Circuit and Spec a 2500W UPS.

In your case a APC Smart-UPS 1500VA would be sufficient IMHO.

https://www.amazon.com/APWSMT1500-APC-Smart-UPS-1500VA-Tower/dp/B009YBP1MI

 

 

 

 

 

 

 

2.4K Posts

November 3rd, 2016 17:00

Thanks to all for your thoughts.

Speedstep, Firstly, he cannot afford an APC Smart-UPS; your link would run him just over $600 CAD. I'm looking at suggesting an APC Back-ups Pro that will handle only his tower/PSU (850 Watts).

Would this unit , -which has basically the same wattage as the PSU (865/850)-, with the proviso that his wattage draw doesn't exceed 80 % when an outage hits, be safe and effective ?:

www.amazon.ca/.../B003Y24DEU

Because I don't understand how these things work I am concerned that I don't hand him a time bomb that may take out his tower or worse by being under-powered.

btw, The PSU people, EVGA, said not to go higher than 1500 VA.

Comment ?

9 Legend

 • 

47K Posts

November 4th, 2016 10:00

That really cheap unit is not pure sine wave and likely a fire bomb waiting to happen. It would neither be safe nor effective.  You cant say wattage draw would be 80 percent.  The power draw will be 20 percent more than maximum due to power loss.  You put 1000W in you get 800W out.  Nobody makes power supplies that are 99.99 percent efficient.  12.5 amps ac is 1500VA  more than that requires a nema 5-20 power cord and outlet aka 20A circuit.

Based on price this is the MINIMUM I would recommend.

It will give you 5 minutes run time.

https://www.amazon.com/Tripp-Lite-Display-Protection-SMART1500LCDT/dp/B009TZTGWK/

Also comes with Insurance against damage.

Your local licensed bonded insured electrician would put one in

where the outlet looks like this.  Which would be the plug for a 2000VA UPS.   2500VA and up would need a L14 30R plug at 208V 30A.

 




 

2.4K Posts

November 4th, 2016 18:00

The Tripplite uses PMW which apparently is the equivalent of step technology. Correct ? If so I don't see what's gained over the APC unit. The Cyberpower does have a pure sine wave and I appreciate that benefit. Why the change ?

btw, We use 15 amp, 120 volt for most electrical here.

2.4K Posts

November 8th, 2016 07:00

Thankyou for sharing  your expertise on a very difficult and poorly understood subject. I feel more confident in passing this along and selecting a viable unit.