Battery selftest not starting in 2700 UPS

Hi all,

hopefully this is the right place for the following question:

Followed the instructions in the user guide for manuall initiating a ups battery test, but nothing happens - control menu, battery test, schedule battery self test:yes...

Would like to do this because i believe, that the automatical self test after battery replacement didn't work.

UPS Status in the NMC states: "battery Charge Level: resting" and "battery Status: aborted".

Any help or hint is highly appreciated!

Regards, David

2 Posts

September 28th, 2015 00:00

Nobody, who can give me a hint regarding this issue?

Regards, David

April 27th, 2016 09:00

Battery self-test requires the load on the computer to be (I believe) greater then 15% and the battery full charged in REST mode. If the load is less than 15% OR the battery is not in REST then battery self-test will not initiate.