PowerEdge R730xd cooling / fan noise issue

Hello all,

About a month ago I updated my client's R730xd, I hadn't updated BIOS, IDRAC etc in quite a long time. After that my client started complaining about excessive noise coming from the server room. The fans were running around 10.5k RPM, which is excessive. I talked to the local Dell support and they suggested disabling C1 states in BIOS. It had a very minor effect, now the fans are around 9.8k RPM.

I have tried disabling the aggressive cooling policy for third party installed PCIe devices via ipmi over LAN, but it had no effect. I don't think there are any third-party PCIe devices, but there are a couple of non-certified SSDs.

Anything else I can try?

 

  • Dell-DylanJ

    6 Operator

    •

    2924 Posts

    8293

    0

    Posted January 14th, 2019 07:00

    Hello,

    The fan speed you listed is within operational allowances, so there may not be any options. However, you might try restarting the iDRAC with racadm racreset -h. The iDRAC functions as a fan controller so restarting it may help. If that fails, you can try performing a power drain by shutting the server off, unplugging it, and holding the power button down for about 30 seconds. If the fan keeps running at a high RPM, the firmware may be doing it deliberately. I did find a link when searching the forum that might help you with some IPMI commands. You can compare what you have with what they used. I can't recommend this though, as it may lead to insufficient cooling and problems arising from that. I don't think you can set maximum cooling speeds, but you may check in the location listed in the owner's manual for thermal control options: https://www.dell.com/support/manuals/us/en/04/poweredge-r730xd/r730xd_ompublication/changing-the-thermal-settings?guid=guid-6aa43bf5-38bb-49c3-9f28-adba64d3ac88&lang=en-us

    https://serverfault.com/questions/715387/how-do-i-stop-dell-r730xd-fans-from-going-full-speed-when-broadcom-qlogic-netxtr/733064#733064

  • Fwiler1

    3 Posts

    7908

    1

    Posted May 16th, 2019 08:00

    I just wanted to say that after updating bios and idrac firmware on our R730xd, I too had full speed fans.

    The solution provided above worked for me, which was power down the system.  Unplug power cords.  Hold power button for 30 seconds.

    After re-plugging power cords and starting up, no problem.

  • DrVille

    3 Posts

    4489

    0

    Posted March 15th, 2021 13:00

    Hi, 

    I have two PowerEdge R730xd and I have a problem with the first one for the ventilation (always run at 87%). The two servers have the same version of firmware and the same revision of the system. 

    - I restarted the iDRAC with racadm racreset -h and I tried the unplug power with the hold power button. 
    - I changed the thermal profile in the iDRAC but I still have the problem. 

    Any idea that I can try to solve the issue?

    Thanks

  • DELL-Young E

    Moderator

    •

    5421 Posts

    •

    37 Points

    4473

    0

    Posted March 15th, 2021 18:00

    Hi, to see why your fan is running so fast we would have to compare your system to another one for number of cards plugged to the riser slots (or the type of cards) and how BIOS settings are different, too.

    Social Media and Communities Professional

    Dell Technologies | Enterprise Support Services

    #IWork4Dell

    Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!

  • Dell-DylanJ

    6 Operator

    •

    2924 Posts

    4416

    0

    Posted March 18th, 2021 13:00

    Understanding why the two system's are cooling differently really isn't something we can get into, because it is firmware controlled and influenced by numerous internal and external factors. The best recommendation we can make is to make sure your firmware and OS are up to date. Considering the concern is cooling, I would review all firmware in the system, not just the BIOS.

  • DrVille

    3 Posts

    4422

    0

    Posted March 18th, 2021 13:00

    Hi, 

    I compared the two servers and here are the differences: 

    - CPU Xeon ES-2640 for the server in problem instead of ES-2650. 

    - RAM running at 2133Mhz but could be at 2400Mhz (Micron MTA18ASF2G72PDZ-2G3B1). The other server run at 2400Mhz but it's not the same model (Hynix). 

    - ESXi is installed on USB drive instead of SD Card. 

    - I can start the Console only with Internet Explorer instead of Chrome. 

    - In LifeCycle: Disk version is PT51 instead of EB01 but it's not the same HDD. 

    All of the settings or version or hardware are the same. 

    - In LifeCycle, the fans run at 45% instead of 25%. 

    - In LifeCycle / System / IDSDMRollupStatus = I have nothing instead of OK. 

    When ESXi start the loading of the software, the fans goes to 87%... It's ESXi 6.7.0 build 15820472 Dell profile image. 

    Thanks for your help. 

  • DrVille

    3 Posts

    4175

    0

    Posted April 1st, 2021 12:00

    Hi, 

    I try again the firmware update with the last Server Update Utility (SUU-WIN64_20.12.200.458) and all the firmware are up to date. 

    Anything else that I can verify? 

    Thanks

  • DELL-Josh Cr

    Community Manager

    •

    9734 Posts

    •

    44224 Points

    4169

    0

    Posted April 1st, 2021 13:00

    Not without removing the non validated SSDs. It is possible that is what is causing the higher fan speeds and there is not a validated method for changing it. 

  • YJjoe

    1 Rookie

    •

    4 Posts

    1938

    0

    Posted April 6th, 2022 12:00

    take a look there

     

    In short:

    Set Third-Party PCIe Card Default Cooling Response Logic To Disabled:

    ipmitool raw 0x30 0xce 0x00 0x16 0x05 0x00 0x00 0x00 0x05 0x00 0x01 0x00 0x00 

     

    You need to make sure IPMI is enabled in iDrac. Install openIpmi in your system OS. 

  • KDSLLC

    3 Posts

    138

    0

    Posted February 6th, 2023 09:00

    I did the IPMI trick but the fans only drop to a normal speed for about 2 seconds, then ramp back up again to 46%.
    The 730xd does not work correctly with non-Dell drives.