CMC Failover causes excessive CPU Load

We have multiple m1000e Chassis units in our datacenter, and they are all full of M610 units. We have now had multiple instances where for some reason, the primary CMC Heartbeat is lost, triggering a CMC failover event. As soon as the second CMC fails over, many of the M610s in that chassis suddenly spike up in CPU usage and become nearly unresponsive. Once we fail back over to the primary CMC, they calm back down. 

We have verified that all power settings are correct and that the CMC firmwares are the same version. The M610s are all running RHEL 6.

Has anyone else had this happen? Is there an update/patch somewhere that resolves this?  We've gone so far in one chassis as to pull the redundant CMC out and run on one until we can figure out the fix.

12 Elder

 • 

6.2K Posts

May 7th, 2015 14:00

Hello

Have you tested the system running just the secondary CMC?

If the system does not have a functional CMC then there are many things that occur. One of the effects of not having a functional CMC is that the blades will run on a low power mode to conserve energy and reduce thermal output since the CMC is not present to manage and monitor power and cooling.

Your scenario sounds like the primary CMC is failing for some reason and the secondary CMC is not functioning properly. I would troubleshoot this as being either a CMC or CMC slot issue. Test the secondary CMC in the primary slot to see if it functions normally. If it functions normally then test the system running off just a CMC in the secondary slot. If the system does not function correctly with either CMC in the secondary slot then you likely have an issue with the secondary slot.

Thanks

4 Posts

May 7th, 2015 15:00

When the CMC fails over to secondary, we are able to log in and manage everything. It appears both CMCs are working properly.  Unfortunately our data center is 200 miles away from the office and so it's hard for us to troubleshoot with switching out slots.

So based on the information you gave me, that would mean the secondary CMC may be faulty in some way, and the servers are running on the low power mode? Even though we can still log into the CMC, it could still be faulty? Is there anyway to test the functionality of the CMC?

12 Elder

 • 

6.2K Posts

May 7th, 2015 15:00

If everything is registering fine with the CMC and no errors are reported then no. Check the CPU frequency within the OS. If the CPU frequency is low then it is being throttled. This could be a CMC or ACPI issue. The blades should not have an issue with ACPI since the CMC failover shouldn't be detected at an OS level.

If throttling is occurring then CPU performance states should be throttled down. That could be the reason CPU usage is hitting 100%. You should be able to see that from within the OS.

Thanks

4 Posts

June 4th, 2015 20:00

So as an update, we had another failover tonight. We had THREE chassis (not in the same rack) that failed within 10 minutes of each other. In two of those chassis, All servers had load spikes and tipped over. As soon as we failed back over the CMCs, load dropped. Is there some setting we aren't finding somewhere that will disable this? I don't care if the CMCs flop back and forth all day, as long as our MISSION CRITICAL boxes stay alive and well.

12 Elder

 • 

6.2K Posts

June 5th, 2015 11:00

You need to review the logs to get an idea of what is going on.

Is there some setting we aren't finding somewhere that will disable this?

Disable what, disable throttling?

http://www.dell.com/support/Manuals/us/en/19/Topic/dell-cmc-v5.0-m1000e/CMCM1000e5.0_UG-v1/en-us/GUID-4C648550-470A-43B7-A18B-876B50ABA851

No, you cannot disable throttling that occurs during CMC failover or if no CMC is present. If you want to resolve the issue then you need to troubleshoot the issue.

  • Pull and review logs
  • Restart one of the servers when this happens to find out if it is an ACPI issue within the OS during the failover

You should also try to remember when this issue started occurring and what changes were made at that time. It sounds like you have multiple chassis across multiple racks that are having this issue. Are all of them running the same CMC firmware? What version is the firmware? When all of these chassis experienced the issue within 10 minutes of each other what was going on? Were they performing a backup, was there a network issue at the site, or anything else that could help narrow down the cause.

You have two issues that you are troubleshooting. Issue number one is why the failover is taking place. The second issue is why throttling continues after the second CMC comes online, that is assuming that the performance issue on the servers is due to throttling. Have you checked the CPU frequency while the systems are having performance issues?

Thanks