Hi

We are performing some stress tests as preparation of a Oracle DWH environment.

The whole configuration is:

VMAX 20K ( is an older model assimilated to 20K ). 5 engines. FC 600 10K disks, SATA 2TB 7200, and EFD 200gb.FAST is configured.

The DWH volume configuration ( TDEV ) for testing is  12 500GB striped metas bound to FC pool. NO FAST policies applied to them.

From the FA point of view, we have 8 ports dedicated, and connected to 2 CISCO MDS 9513 ( one per fabric ), that own a linecard X-DS9248-96K9, that support 8GB. The port speed has been configured as fixed 8G

From the host point of view, we have a cluster of 2 members that are connected too to the CISCO MDS 9513, and the same linecard. Every host in every fabric have 2 initiators. PowerPath with the SymmOpt policy is configured there.

Port configuration in the linecard is as follows:

1,7,13,19 : HOST

25,31,37,43: VMAX

It means that only the first port of every port group is used. All ports are configured to 8GB and dedicated, so, as per CISCO documentation, we have warranty about that all ports have reserved the 8GB. In fact, in nominal values, we should obtain more or less 800-850MB/s in all ports

Based on this configuration, should obtain a similar rate when use the FIO Linux tool,, but, we obtain a surprising low bandwith on the Symm side:

FIO CONFIGURATION:

[global]
bs=1024k
direct=1
rw=read
ioengine=libaio
iodepth=64
zonesize=4g
zoneskip=4g

[/dev/emcpowerkn]
[/dev/emcpowerko]
[/dev/emcpowerkp]
[/dev/emcpowerkq]
[/dev/emcpowerkr]
[/dev/emcpowerks]
[/dev/emcpowerkt]
[/dev/emcpowerku]
[/dev/emcpowerkv]
[/dev/emcpowerkw]
[/dev/emcpowerkx]
[/dev/emcpowerky]

1 host - 1 storage : 350-375MB /s. This is similar result that we obtain when used 4GB ports.

1 host - 2 storage : 700MB/s. It means that the host side is able to go near to the nominal bandwith, and in this case, powerpath is dividing the storage bandwith ( 350+350 )

1 host -3 storage: near to 800MB/s. 270MB/s obtained in the symmetrix ports

1 host -4 storage: near to 800MB/s. 200MB/s obtained in the symmetrix ports

Observed that FA port %busy is low, FA % busy is low ( below 30% ), but response time is growing up to 300 ms.

When repeat the same test using 2 host ports, the limit in the symmetrix ports is always in 375-400MB/s, never go up.

Confirmed with CISCO team that there is no restriction on por side.

In fact, before to use the 8 FA dedicated FA ports in the 8G linecard, performed same test using 16 shared FA ports connected to 4G switch ports. Configuration was 1 host -- 2 FA, and obtained the desired result: 700MB/s per port, 5400-5600MB/s global, so we are not observing backend limitation.

Opened SR's with CISCO and VMAX teams, but didn't found the required answers..

So, the questions.....

What's the nominal bandwith that should expect from VMAX side? Why we are not getting it?

All collaboration will be appreciated


  • Quincy561

    1281 Posts

    913

    0

    Posted June 6th, 2013 06:00

    The front end IO module on the 20K is limited to around 600MB/sec.  This is 4 FA ports.  E+F share and IO module and G+H share the others.  You should make sure these hosts are spread over as many IO modules as possible.

  • 913

    0

    Posted June 6th, 2013 08:00

    Hi Quincy

    Many thanks for your quick answer.

    Based on this limit, we have checked our port distribution.

    FabricA

           FA-3G:0
           FA-4G:0
           FA-3H:1
           FA-4H:1
    FabricB

          FA-7E:1

           FA-10E:1

           FA-5H:1

           FA-6H:1

    Obviously, in FabricA we have this limit.

    So, tested again using only the FabricB ports. But got the same results, more or less 350-400MB/s per port.

    Now we are checking the IO Modules.

    As this is a VMAX system, older tan VMAX20k series, do you know if the IO Modules for the older systems have the same limitation? Or have less bandwith.

    Or, better, where we can find the values for the different ( if are ) VMAX IO Modules?

    Thanks again in advance.

  • Quincy561

    1281 Posts

    913

    0

    Posted June 6th, 2013 09:00

    Also a very good tool for driving IO from Unix systems is IORATE.  You can download it from iorate.org


  • Quincy561

    1281 Posts

    913

    0

    Posted June 6th, 2013 09:00


    3G and 4G are on different directors and don't share the same IO module.

    It is possible that something else is the bottleneck for throughput, such as disk drives or DAs.

    Without data, I can't say what your bottleneck is.

  • Quincy561

    1281 Posts

    913

    0

    Posted June 6th, 2013 09:00

    You may want to start with 100% "hit" tests with 64-128K IOs to see what you can get.  Very small data sets are useful to do this.