Moving to a new UPS
The UPS where my VNXe is telling me it is failing. Currently, both power supply are connected to a single UPS. I wanted to power my VNXe using 2 separate UPS going forward. I am hoping that I don't need to schedule any downtime to do this. Since there are 2 power supply, am I correct in assuming that I can unplug one power supply, say DPE Power supply B and plug it to a new UPS without powering down the whole DPE? After a few minutes, I will unplug the Power supply A from the old UPS and plug it to another new UPS. Will that cause any problem?
Thanks
Vince
No Events found!


brettesinclair
2 Intern
•
715 Posts
0
April 8th, 2015 16:00
Yes, the Power supplies are shared and redundant. If one fails or you move it's power source, the surviving one provides power to both SP's.
When you move PS-B to the new UPS, wait until any fault conditions (leds) normalize then do the other. As you've said, a few minutes should be sufficient.
VinceTan
1 Rookie
•
12 Posts
0
April 10th, 2015 06:00
Thanks. Working perfectly