We have a PowerEdge 1950 that I recently replaced one of the PSU's on. When it booted back up, the amber light on the back was still lit. I pressed the button next to the "i" on the back and the light turned off.
The server powers on without issue and is not displaying any error codes, however now the indicator lights on both the front and back are blank. No blue or amber. Pressing the "i" button on either side does nothing.
I've powered down the device, disconnected both PSU's, and drained the server of power by holding the power button but no change.
Is there a setting that may be causing the "i" lights and LCD display to not light up, or did something get fried?
See if the rear button got stuck in when you pressed it earlier.
Reseating the cables is a good first step for troubleshooting.
Review the BIOSduring POST
Choose - Embedded Server Management
Displays a screen to configure the front-panel LCD options and to set a user defined LCD string.
See what settings are available. The manual is lacking on the deeper menu on this
Similarly during POST enter the BMC/DRAC 5 +
See if you have LCD configurationSee what settings are available. The manual is lacking on the deeper menu on this
Next you can try Clear NVRAM -Shut down,Set jumper to the Clear position, power on and Post up to the jumper error, shut down and return to original location.
If you have any custom BIOS settings you may have to reset those after clearing.
DELL-Charles R
Moderator
•
4730 Posts
•
25476 Points
663
0
Posted March 30th, 2022 13:00
Hello pdechen,
I would first recommend reseat:
Shut down, Reseat cables at control panel and system board. Check for damaged connectors and cable.
Control Panel Assembly page 88
Owners manual : https://dell.to/3DqWhUz
DELL-Charles R
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Accept as Solution’. ‘Thumbs up’ the posts you like!