UPS 3750 Voltage

So I have a 3750W UPS (208V plug model) that has been running happily in a facility with 208V.  I am moving this UPS to a location that has only 230v.  I understand the input voltage is rated up to 255v on this unit, but will it still function normally at 230?  

  • Daniel My

    12 Elder

    6205 Posts

    865

    0

    Posted July 9th, 2019 15:00

    Hello

    I suggest reviewing documentation. I think this is the support page for the UPS.

    https://www.dell.com/support/home/product-support/product/dell-online-rack-ups-3750r/research

    As long as the input is the appropriate type, AC or DC, and is providing voltage and amperage that is within supported specifications then it should work.

    Thanks

  • adk_mechetech

    1 Rookie

    10 Posts

    853

    0

    Posted July 9th, 2019 18:00

    I actually just figured out how to do it through the front panel.  I was confused how to actually get into the menus there.   I was able to change the output voltage from 208 to autosense and everything seems to be peachy now.  The units (I actually have 2) are happily running alarm free in bypass mode. 

     

  • adk_mechetech

    1 Rookie

    10 Posts

    857

    0

    Posted July 9th, 2019 18:00

    I did actually read the manual, that's where I got the number for max voltage I mentioned.  

    Nowhere in the manual(s) did I find it mention anything about setting input voltage thresholds like I can do with my APC units.  I am not very familiar with these dell units and did not originally set them up.  

    What I found when I powered the unit up with 240VAC is that they will not go to bypass mode.  The input voltage is too high.  The output still works fine, however it is regulated down to 208.  It would be nice if there were settings somewhere I could change.

    I did find the pinout for the serial cable I think, maybe config is there?

  • Origin3k

    6 Operator

    2421 Posts

    12396 Points

    850

    0

    Posted July 9th, 2019 19:00

    Youre using an old Dell (Eaton based) 3750 Watt UPS which goes end of sale 4 years ago.  We have 3 dozen of them left in production and they all run on 230V here.

    Regards,
    Joerg

  • 399

    0

    Posted December 27th, 2022 15:00

    Hello,

    I know this is an older thread but I was hoping someone might still be able to answer a question for me.

    Can anyone tell me if these could be used in a residential environment using either 120v or 220v (which is actually 240v)?

    I greatly appreciate any information!

    -Sam

  • adk_mechetech

    1 Rookie

    10 Posts

    387

    0

    Posted December 27th, 2022 16:00

    It works just fine.  Make sure you don't have any loads connected when you power it in. You will need to go into the menus and set the correct input and output voltage and tolerances.

    I have had 2 running perfectly on 240v single phase since I started this post.  I recently acquired 2 more that I plan to hook up the same way. 

  • adk_mechetech

    1 Rookie

    10 Posts

    381

    0

    Posted December 27th, 2022 18:00

    Why do you say that? 

    Genuinely curious, as they are well within their ratings.  I realize it's not a "standard" installation, but we aren't running anything out of spec. 

  • DELL-Young E

    Moderator

    5421 Posts

    37 Points

    382

    0

    Posted December 27th, 2022 18:00

    Hello, I would highly advise AGAINST it. Good chance of fire.

    Social Media and Communities Professional

    Dell Technologies | Enterprise Support Services

    #IWork4Dell

    Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!

  • adk_mechetech

    1 Rookie

    10 Posts

    299

    0

    Posted December 27th, 2022 21:00

    OK.... Pg63 doesn't have any useful information.

    "because I said so" doesn't mean . TOS76>

    .  Just because it's not an "approved" installation, doesn't automatically mean it's a safety hazard.  If you look at the speciations/ratings of the equipment, and have half a brain to interpret them, there should be no adverse effect running on 240v single phase.  It is not explicitly prohibited.  If it were so dangerous, why is it not called out as such in the documentation? 

  • DELL-Young E

    Moderator

    5421 Posts

    37 Points

    377

    0

    Posted December 27th, 2022 21:00

    It is possible to use but I would still say it's risky and if you don't use the right model it could be damaging to UPS and could lead to fire.

    chrome-extension://efaidnbmnnnibpcajpcglclefindmkaj/https://dell.to/3hT9MpC

    Dell Online Rack UPS 3750W and 4200W User's Guide
    If you look at page 63, table 9 , UPS model list, they are all different.

    Social Media and Communities Professional

    Dell Technologies | Enterprise Support Services

    #IWork4Dell

    Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!