Had drive in slot 7 fail when the box tried to use the hot spare it was also bad so it went into degraded mode
there are also 2 drives in impending failure
first thing I did was replace the drive in slot 7 let it rebuild then replaced the hot spare drive in slot 11 and the system is optimal now and the hot spare is in standby
The issue is that when I try to do a VM backup using Veeam I am getting CRC errors but the servers seem to be running, must just have some corruption.
I am waiting for more spare drives to replace the 2 impending failure drives
can the corruption be repaired or should I just replace the impending drives one at a time when the new drives arrive?
If the drive hasn’t failed yet & you have a free hotspare drive then you can fail the drive in MDSM so that it will start the copy to your hotspare. Once the copy to your hotspare completes then I would replace the drive.
Please let us know if you have any other questions.
abongard
1 Rookie
•
7 Posts
2342
0
Posted December 7th, 2017 11:00
Its an MD3200!