UPS Software

Seeing as there's no UPS category on the forums anywhere this will have to do.

I'm looking for the options to calibrate the runtime on some of our UPS's here with the Dell UPS Local Node Manager.

Seems there's no option to calibrate at all. During our last power outage some of our UPS shutdowns failed, and it appears this is because the UPS ran out of battery charge before issuing a shutdown. What can we do from the server's these UPS are connected to to test this? Most of the sites are remote so pressing buttons on the UPS are out of the question.

  • Michael-H

    1 Rookie

    •

    12 Posts

    1393

    0

    Posted June 27th, 2012 20:00

    As a follow up on UPS software - we have one site that is running the Dell UPS Local Node Manager and the service randomly goes on holiday. It will log the problem as -

    A timeout (90000 milliseconds) was reached while waiting for a transaction response from the Dell UPSLocalNodeManager service

    Its logged approximately every half an hour.

    Once this event starts to be logged the server can no longer see the UPS and so is not getting any shutdown commands, etc.

    Is there a fix for this?

  • 1393

    0

    Posted July 5th, 2012 03:00

    Hi Michael.

    There are quite a few variables that need to be looked at in order to help with troubleshooting.  If you are able to provide information around the following topics it would certainly help:

    -          Computer operating system & revision level
    -          Computer hardware manufacturer & type
    -          MUMC software version level
    -          ULNM software version level
    -          UPS Description (e.g. 2700W Rack/Tower)
    -          UPS PPID (Serial Number)
    -          UPS Firmware Revision Level
    -          NMC Firmware Revision Level
    -          Description of problem
    -          Relevant screenshots

     

  • Michael-H

    1 Rookie

    •

    12 Posts

    1393

    0

    Posted July 8th, 2012 22:00

    Hi Andy

    Heres the details you've requested -

    OS - Windows Small Business Server 2011 Standard. 6.1.7600 build 7600

    system - Dell PowerEdge T710

    MUMC - not installed

    ULNM - Product version: 01.02 build 0006

    UPS - Dell UPS Tower 1920W HV UPS LI T 1920

    PPID - CN-0K789N-75162-1AE-0045-A06

    Firmware - As its connected via USB, I don't know how to retrieve the firmware info for the unit.

    problem - the Dell ULNM service software stops responding - when you log into the server in this state and mouse over the tray icon the status text will reply - UPS unreachable. The event log records this -

    "A timeout (90000 milliseconds) was reached while waiting for a transaction response from the Dell UPSLocalNodeManager service."

    Restarting the service fixes this - if you are logged on. Restarting the service via scheduled task results in the same errors being logged.

    It seems to be erratic for the service failure - it can go days without logging it, other times it;ll do it a couple of times a day.

    Once the error has been logged the system is no longer in contact with the UPS, and won't get gracefully shutdown via the UPS during power outages etc.

    As a side note - we don't know how to run a calibration on these UPS from the ULNM. We have one UPS that is over estimating its run time by abot an hour, causing a few headaches. Is there any solution for this?

  • Michael-H

    1 Rookie

    •

    12 Posts

    1393

    0

    Posted July 10th, 2012 22:00

    screenshots as requested








  • 1393

    0

    Posted July 11th, 2012 02:00

    Hi Michael

    Thanks for the additional information.  It does not appear to be something seen before.  If possible, can you enable debug mode in the software and post the results?

    How to enable debug mode:

    1)      Stop the running Dell ULNM instance.
    2)      Enable debug mode by modifying the file ‘C:\{ULNM_INSTALLATION_PATH}\Dell\UPSLocalNodeManager\configs’ as shown below (red parts)
    3)      Start ULNM service.
    4)      Play with the software until the issue appears.
    5)      Retrieve and send the obtained log files, that should be available in ‘C:\{ULNM_INSTALLATION_PATH}\Dell\ UPSLocalNodeManager \’ as ‘run_{day_date_hour}.log’ files.

    cfg =

    {

      'enabled': true,

      'maxKBytes': 1024,

      'baseFileName': "run_{0}.log",

      'verbose':

      {

        'NodeManager': 1,

        'ShutdownManager': 1,

        'TaskManager': 1,

        'ScanManager': 1,

        'Scan': 1,

        'ServiceManager': 1,

        'VMHostManager': 0,

        'VMwareWebService': 0,

        'CitrixWebService': 0,

        'azertyuiop': 0,

        'HIDLayer': 0,

        'HIDParser': 0,

        'SHUT': 0,

        'USB': 0,

        'XCP': 0,

        'XCPSerial': 0,

        'XCPUSB': 0,

        'UNMPService': 0,

        'ConfigManager': 0,

        'EventManager': 0,

        'FirmwareManager': 0,

        'LogManager': 0,

        'UpdateManager': 0,

        'ViewManager': 0,

        'HTTP-Server': 0,

        'HTTPS-Server': 0,

        'SMTPClient': 0,

        'DB': 0,

        'XMLNotifyService': 0,

        'XMLAlarmService': 0,

        'XMLProxy': 1,

        'TFTPService': 0

      }

    }

     

     

     

     

  • Michael-H

    1 Rookie

    •

    12 Posts

    1393

    0

    Posted July 12th, 2012 20:00

    Heres some of the logs for the incident. We enabled the restart task to restart the service every half an hour and found it was logging the faults - however at some stage overnight the log files stopped being generated. When I connected back to the server in the morning the service was having problems though. Heres the output of the systray.log first ( I restarted the service after connecting to the server, as you can see when it comes online)

    2012/07/13-09:32:39.121 | Systray          | Read config from 'C:\ProgramData/Dell/systray.adm1n-mngmt.cfg' ->

    {

     'x': 467,

     'y': 284,

     'w': 520,

     'h': 307

    }

    2012/07/13-09:32:40.728 | Systray          | Update

    2012/07/13-09:33:39.863 | Systray          | Answer: "503"

    2012/07/13-09:33:39.865 | Systray          | Systray.serverUnreachable: true

    2012/07/13-09:34:45.370 | Systray          | Answer: "503"

    2012/07/13-09:34:45.372 | Systray          | Systray.serverUnreachable: true

    2012/07/13-09:35:50.879 | Systray          | Answer: "503"

    2012/07/13-09:35:50.882 | Systray          | Systray.serverUnreachable: true

    2012/07/13-09:36:56.388 | Systray          | Answer: "503"

    2012/07/13-09:36:56.391 | Systray          | Systray.serverUnreachable: true

    2012/07/13-09:38:01.898 | Systray          | Answer: "503"

    2012/07/13-09:38:01.901 | Systray          | Systray.serverUnreachable: true

    2012/07/13-09:38:13.233 | Systray          | Answer: "503"

    2012/07/13-09:38:13.236 | Systray          | Systray.serverUnreachable: true

    2012/07/13-09:38:19.251 | Systray          | Answer: "200"

    2012/07/13-09:38:19.254 | Systray          |

    {

     'date': 1342143498747,

     'events':

     [

     ],

     'powerSource': "CN-0K789N-75162-1AE-0045-A06",

     'status':

     {

       'System.Name': "Dell UPS Tower 1920W HV UPS LI T 1920",

       'UPS.PowerSummary.PresentStatus.ACPresent': 1,

       'UPS.PowerSummary.RemainingCapacity': 100,

       'UPS.PowerSummary.RunTimeToEmpty': 2160,

       'Local.RunTimeToShutdown': -1,

       'System.CommunicationLost': 0,

       'UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit': 0,

       'UPS.PowerSummary.PresentStatus.InternalFailure': 0,

       'UPS.PowerSummary.PresentStatus.Overload': 0,

       'UPS.PowerSummary.PresentStatus.Good': 1,

       'UPS.OutletSystem.Outlet[2].PresentStatus.SwitchOnOff': 1,

       'UPS.OutletSystem.Outlet[3].PresentStatus.SwitchOnOff': 1,

       'UPS.PowerSummary.PresentStatus.NeedReplacement': 0,

       'UPS.PowerSummary.PresentStatus.ShutdownImminent': 0

     }

    }

    Heres a full log of one running instance of the UPS service. run log. Some of the run logs are missing - the ones that are missing coincide with reports of a transaction timeout. This short log shows what looks to be the service running normally, at the time no transaction timeouts are reported..

    2012/07/12-12:42:03.490 | run.js           | Run UPS Local Node Manager v01.02 build 0006

    2012/07/12-12:42:03.615 | NodeManager      | Load 2 node(s) from database...

    2012/07/12-12:42:03.623 | NodeManager      | Load driver: 'scripts/drivers/ups_pdc.js'

    2012/07/12-12:42:03.631 | NodeManager      | Init node ('ups_pdc'): 'CN-0K789N-75162-1AE-0045-A06'

    2012/07/12-12:42:03.643 | NodeManager      | Load driver: 'scripts/drivers/nmc.js'

    2012/07/12-12:42:03.652 | NodeManager      | Init node ('nmc'): '192.168.19.199'

    2012/07/12-12:42:03.833 | TaskManager      | Run task: 'Load Stats' on thread[2] / #8624

    2012/07/12-12:42:03.837 | TaskManager      | Run task: 'Load No Acks' on thread[4] / #31508

    2012/07/12-12:42:03.842 | NodeManager      | Node Manager ready...

    2012/07/12-12:42:03.845 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:42:03.847 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> init' on thread:emotion-29: / #6740

    2012/07/12-12:42:03.850 | CN-0K789N-75162-1AE-0045-A06 | Init UPS driver for node 'CN-0K789N-75162-1AE-0045-A06'

    2012/07/12-12:42:03.957 | TaskManager      | Run task: '[192.168.19.199] -> init' on thread[7] / #39984

    2012/07/12-12:42:04.338 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[7] / #39984

    2012/07/12-12:42:04.869 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getProductInfo' on thread[7] / #39984

    2012/07/12-12:42:04.903 | CN-0K789N-75162-1AE-0045-A06 | Device 'CN-0K789N-75162-1AE-0045-A06' not found...

    2012/07/12-12:42:04.938 | ScanManager      | scanSerialNode: USB

    2012/07/12-12:42:05.220 | ScanManager      | USB new device list:

    [

     /*0:*/

     {

       'idVendor': 1148,

       'idProduct': 65535,

       'dirName': "bus-0",

       'fileName': "\\\\.\\libusb0-0001--0x047c-0xffff",

       'hid': 1

     }

    ]

    2012/07/12-12:42:05.244 | ScanManager      | USB device list:

    {

    }

    2012/07/12-12:42:05.473 | TaskManager      | Run task: '[192.168.19.199] -> getProductInfo' on thread:emotion-29: / #6740

    2012/07/12-12:42:05.632 | ScanManager      | Found USB device:

    {

     'idVendor': 1148,

     'idProduct': 65535,

     'dirName': "bus-0",

     'fileName': "\\\\.\\libusb0-0001--0x047c-0xffff",

     'hid': 1,

     'opened': true,

     'connection': {object},

     'mode': "HID_USB",

     'hidLayer': {object},

     'handle': 79677160,

     'connected': true,

     'id': "CN-0K789N-75162-1AE-0045-A06"

    }

    2012/07/12-12:42:05.657 | ScanManager      | scanSerialNode: SERIAL

    2012/07/12-12:42:05.730 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:42:05.945 | TaskManager      | Run task: 'Auto notification' on thread[9] / #38128

    2012/07/12-12:42:06.009 | ScanManager      | addScanList 192.168.19.250

    2012/07/12-12:42:06.046 | TaskManager      | Run task: 'ScanManager.runScanList' on thread[9] / #38128

    2012/07/12-12:42:06.049 | ScanManager      | runScanList count 1 / 1 -> 0%

    2012/07/12-12:42:06.069 | TaskManager      | Run task: 'Discover Node [192.168.19.250]' on thread[10] / #29416

    2012/07/12-12:42:06.368 | ScanManager      | Scan [192.168.19.250] found 'MAINSERVER.domain.local' -> 'ipp'

    2012/07/12-12:42:08.861 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-12:42:10.760 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:42:13.859 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:42:14.724 | ScanManager      | SERIAL new device list:

    [

    ]

    2012/07/12-12:42:14.727 | ScanManager      | SERIAL device list:

    {

    }

    2012/07/12-12:42:14.960 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getProductInfo' on thread[7] / #39984

    2012/07/12-12:42:14.964 | CN-0K789N-75162-1AE-0045-A06 | Assign USB device:

    {

     'idVendor': 1148,

     'idProduct': 65535,

     'dirName': "bus-0",

     'fileName': "\\\\.\\libusb0-0001--0x047c-0xffff",

     'hid': 1,

     'opened': true,

     'connection': {object},

     'mode': "HID_USB",

     'hidLayer': {object},

     'handle': 79677160,

     'connected': true,

     'id': "CN-0K789N-75162-1AE-0045-A06"

    }

    2012/07/12-12:42:15.010 | HIDLayer         | Report descriptor size: 1795

    2012/07/12-12:42:15.862 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:42:19.308 | CN-0K789N-75162-1AE-0045-A06 | node.data.shutdownCapabilities=

    {

     'shutoffAllowed': true,

     'authenticationRequired': false,

     'loadSegmentEditable': false,

     'loadSegmentAvailable': "1,2,3"

    }

    2012/07/12-12:42:19.312 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:20.964 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:42:20.967 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:20.970 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:42:21.410 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:42:21.419 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:42:21.766 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:21.862 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[7] / #39984

    2012/07/12-12:42:21.865 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:42:23.964 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:42:26.065 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:42:26.069 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:42:26.072 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:42:26.930 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:42:26.935 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 518 -> level: 0

    2012/07/12-12:42:26.941 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 518

    2012/07/12-12:42:26.944 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 593 -> level: 0

    2012/07/12-12:42:26.950 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 593

    2012/07/12-12:42:26.953 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.5 -> level: 0

    2012/07/12-12:42:26.959 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.5

    2012/07/12-12:42:26.962 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1402

    2012/07/12-12:42:26.966 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097595

    2012/07/12-12:42:26.969 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> restartOutlets' on thread:emotion-29: / #6740

    2012/07/12-12:42:26.971 | CN-0K789N-75162-1AE-0045-A06 | Restart outlets task for node 'CN-0K789N-75162-1AE-0045-A06'

    2012/07/12-12:42:26.974 | CN-0K789N-75162-1AE-0045-A06 | Check outlet#2 state: 1

    2012/07/12-12:42:26.976 | CN-0K789N-75162-1AE-0045-A06 | Check outlet#3 state: 1

    2012/07/12-12:42:27.079 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:42:27.083 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:27.866 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 236 -> level: 0

    2012/07/12-12:42:27.875 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:42:27.898 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:28.881 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-12:42:31.084 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:42:31.088 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:42:33.182 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:42:33.185 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:33.630 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-12:42:33.889 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:42:33.902 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 235 -> level: 0

    2012/07/12-12:42:33.909 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:42:33.982 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:42:33.997 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:36.185 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:42:36.189 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-12:42:36.192 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-12:42:39.285 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:42:39.288 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:40.075 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:41.285 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:42:41.289 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-12:42:44.083 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:42:45.384 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:42:45.387 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:45.840 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:42:46.112 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:42:46.185 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:42:46.208 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:46.381 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:42:46.385 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:42:46.387 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:42:48.990 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:42:51.483 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:42:51.487 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:42:51.486 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:42:51.492 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:51.868 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.PercentLoad == 31 -> level: 0

    2012/07/12-12:42:51.876 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:42:52.211 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:42:52.285 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:42:52.308 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:42:54.191 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:42:56.584 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:42:56.588 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:42:57.590 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:42:57.593 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:42:57.969 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:42:58.300 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:42:58.394 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:01.687 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:01.691 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:03.685 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:03.688 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:03.984 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:43:04.286 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:43:04.376 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-12:43:04.391 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:43:04.464 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:43:04.488 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:06.783 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:06.786 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:09.088 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:43:09.791 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:09.794 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:10.499 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:43:10.574 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:43:10.597 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:11.890 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:11.894 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:14.387 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:43:15.890 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:15.893 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:16.610 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:43:16.683 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:43:16.707 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:16.990 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:16.994 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:21.887 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-12:43:21.890 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:43:22.090 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #29416

    2012/07/12-12:43:22.094 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:24.488 | TaskManager      | Run task: 'Flush DB' on thread[10] / #29416

    2012/07/12-12:43:26.924 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:43:26.928 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Frequency == 50 -> level: 0

    2012/07/12-12:43:26.934 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 50

    2012/07/12-12:43:26.937 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-12:43:26.943 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-12:43:26.946 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 510 -> level: 0

    2012/07/12-12:43:26.952 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 510

    2012/07/12-12:43:26.954 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 577 -> level: 0

    2012/07/12-12:43:26.960 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 577

    2012/07/12-12:43:26.963 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.4 -> level: 0

    2012/07/12-12:43:26.969 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.4

    2012/07/12-12:43:26.972 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Frequency == 50 -> level: 0

    2012/07/12-12:43:26.978 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Frequency' = 50

    2012/07/12-12:43:26.981 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1410

    2012/07/12-12:43:26.984 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-12:43:26.990 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-12:43:26.994 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097655

    2012/07/12-12:43:26.998 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:43:27.000 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:27.108 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:27.112 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:27.708 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 235 -> level: 0

    2012/07/12-12:43:27.715 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:43:27.781 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 236 -> level: 0

    2012/07/12-12:43:27.789 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:43:27.811 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:29.104 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:43:32.208 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:32.212 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:33.006 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:33.009 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:33.717 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:43:33.791 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:43:33.815 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:34.008 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:43:34.505 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:43:37.312 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:37.316 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:39.109 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:39.112 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:39.816 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:43:39.890 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:43:39.913 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:42.406 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:42.410 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:44.613 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:43:45.214 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:45.217 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:45.926 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:43:46.000 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:43:46.023 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:47.506 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:47.510 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:49.213 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:43:51.306 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:51.309 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:51.683 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:43:52.025 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:43:52.099 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:43:52.122 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:43:52.615 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:43:52.618 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:54.712 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:43:57.412 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:43:57.415 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:43:57.708 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:43:57.712 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:43:57.794 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:43:58.199 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:43:58.222 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:02.816 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:02.819 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:03.511 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:03.514 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:03.876 | TaskManager      | Run task: 'Purge Log' on thread[9] / #38128

    2012/07/12-12:44:04.109 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:44:04.290 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:44:04.313 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:04.816 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:44:04.884 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-12:44:07.908 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:07.912 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:09.314 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:44:09.617 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:09.620 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:10.408 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:13.012 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:13.016 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:14.918 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:44:15.711 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:15.714 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:16.162 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:44:16.169 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:44:16.434 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:44:16.528 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:18.111 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:18.115 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:44:18.118 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:44:21.810 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:21.813 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:22.191 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:44:22.607 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:22.610 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:44:22.613 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:44:23.211 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:23.215 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:44:25.012 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:44:27.671 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:44:27.674 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 522 -> level: 0

    2012/07/12-12:44:27.679 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 522

    2012/07/12-12:44:27.681 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 594 -> level: 0

    2012/07/12-12:44:27.685 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 594

    2012/07/12-12:44:27.686 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.5 -> level: 0

    2012/07/12-12:44:27.690 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.5

    2012/07/12-12:44:27.692 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Frequency' = 49.9

    2012/07/12-12:44:27.694 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1398

    2012/07/12-12:44:27.696 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:44:27.698 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:44:27.700 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:44:27.702 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097715

    2012/07/12-12:44:27.914 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:27.916 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:28.313 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:44:28.317 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:44:28.320 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:44:28.687 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:44:28.711 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:29.414 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:44:33.418 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:33.422 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:44:34.015 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:34.018 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:34.213 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:44:34.462 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:44:34.468 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:44:34.733 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:44:34.827 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:35.120 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:44:38.514 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:38.518 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:38.521 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:44:40.113 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:40.116 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:40.906 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:43.620 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:43.624 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:45.217 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:44:46.217 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:46.220 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:47.006 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:48.720 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:48.723 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:49.515 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:44:52.318 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:52.321 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:52.780 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:44:53.043 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:44:53.116 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:44:53.139 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:44:53.822 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:44:53.826 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:44:53.828 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:44:55.321 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:44:58.423 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:44:58.426 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:44:58.869 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:44:58.917 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:44:58.921 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:44:58.924 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:44:59.141 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:44:59.216 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:44:59.239 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:04.023 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:04.027 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:45:04.320 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:45:04.522 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:04.525 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:04.970 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:45:04.977 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:45:05.241 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:45:05.315 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:45:05.338 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:05.391 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:45:05.421 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:45:09.119 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:09.122 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:45:09.125 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:45:09.618 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:45:10.621 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:10.624 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:11.068 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:45:11.076 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:45:11.425 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:14.220 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:14.224 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:45:14.227 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:45:15.519 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:45:16.723 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:16.726 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:17.168 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 1950 -> level: 0

    2012/07/12-12:45:17.174 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 1950

    2012/07/12-12:45:17.440 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-12:45:17.447 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-12:45:17.514 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-12:45:17.521 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-12:45:17.544 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:19.317 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:19.321 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-12:45:19.324 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1365

    2012/07/12-12:45:22.616 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-12:45:22.619 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:45:24.416 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #29368

    2012/07/12-12:45:24.420 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-12:45:25.623 | TaskManager      | Run task: 'Flush DB' on thread[10] / #29368

    2012/07/12-12:45:27.686 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:45:27.691 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 49.9

    2012/07/12-12:45:27.694 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 235 -> level: 0

    2012/07/12-12:45:27.700 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:45:27.703 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 504 -> level: 0

    2012/07/12-12:45:27.709 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 504

    2012/07/12-12:45:27.711 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 584 -> level: 0

    2012/07/12-12:45:27.717 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 584

    2012/07/12-12:45:27.720 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.4 -> level: 0

    2012/07/12-12:45:27.726 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.4

    2012/07/12-12:45:27.729 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1416

    2012/07/12-12:45:27.731 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 236 -> level: 0

    2012/07/12-12:45:27.737 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:45:27.741 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:45:27.746 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:45:27.749 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097775

    2012/07/12-12:45:27.752 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:45:27.754 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:28.542 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:29.522 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:29.526 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:45:29.529 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:45:29.721 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:45:33.825 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:33.828 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:34.423 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:45:34.537 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:45:34.626 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:45:34.629 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:45:34.632 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:35.724 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:45:39.725 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:39.729 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:45:39.921 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:39.923 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:40.637 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:45:40.730 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:44.824 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:44.828 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:45:45.820 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:45:46.020 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:46.023 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:46.464 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:45:46.470 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:45:46.737 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:45:46.831 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:49.824 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:45:49.927 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:49.930 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:45:49.933 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:45:52.125 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:52.128 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:52.504 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:45:52.836 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:45:52.930 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:45:55.023 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:45:55.026 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:45:55.928 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:45:58.227 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:45:58.229 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:45:58.604 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:45:58.946 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:45:59.020 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:45:59.043 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:00.125 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:00.129 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:46:04.322 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:04.324 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:04.525 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:46:04.774 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:46:05.120 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:05.223 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:05.226 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:46:05.229 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:46:05.401 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:46:06.022 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:46:09.921 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:46:10.325 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:10.329 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:46:10.422 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:10.424 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:10.883 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:46:10.890 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:46:11.155 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:46:11.228 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:46:11.251 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:15.425 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:15.429 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:46:15.431 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:46:16.124 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:46:16.526 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:16.529 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:16.973 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:46:17.329 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:20.522 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:20.526 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:46:20.529 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:46:22.622 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:22.625 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:23.073 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:46:23.419 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:23.423 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:46:23.425 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:46:25.623 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:25.627 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:46:25.630 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:46:26.223 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:46:28.481 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:46:28.486 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 515 -> level: 0

    2012/07/12-12:46:28.492 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 515

    2012/07/12-12:46:28.494 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 593 -> level: 0

    2012/07/12-12:46:28.500 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 593

    2012/07/12-12:46:28.502 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.5 -> level: 0

    2012/07/12-12:46:28.508 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.5

    2012/07/12-12:46:28.511 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1405

    2012/07/12-12:46:28.515 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097836

    2012/07/12-12:46:28.724 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:28.727 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:29.444 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:46:29.518 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:46:29.542 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:30.026 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:46:30.729 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:30.732 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:46:34.626 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:46:34.829 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:34.831 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:35.534 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:46:35.608 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:46:35.631 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:35.824 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:35.827 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:46:36.330 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:46:40.925 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:40.929 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:46:40.932 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:46:40.935 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:41.381 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-12:46:41.727 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:46.033 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:46.037 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-12:46:46.040 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-12:46:46.432 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:46:47.031 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:47.034 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:47.481 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:46:47.827 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:50.130 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:46:51.134 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:51.139 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:46:51.142 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:46:53.135 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:53.138 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:53.843 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:46:53.917 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:46:53.940 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:46:56.233 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:46:56.237 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:46:56.529 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:46:59.231 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:46:59.234 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:46:59.680 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:47:00.025 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:01.328 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:01.332 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:01.335 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:47:04.731 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:47:05.334 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:05.337 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:05.414 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-12:47:06.126 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:06.431 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:06.435 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:06.627 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:47:10.236 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:47:11.430 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:11.433 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:11.536 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:47:11.539 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:11.810 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:47:11.890 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:47:11.896 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:47:12.245 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:16.629 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:16.633 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:47:16.635 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:47:16.728 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:47:17.528 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:17.531 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:17.909 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:47:17.979 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:47:17.985 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:47:18.251 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 231 -> level: 0

    2012/07/12-12:47:18.258 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-12:47:18.325 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 232 -> level: 0

    2012/07/12-12:47:18.331 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-12:47:18.354 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:21.737 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:21.741 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:21.744 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:47:23.438 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-12:47:23.441 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:47:26.828 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #24396

    2012/07/12-12:47:26.832 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:26.828 | TaskManager      | Run task: 'Flush DB' on thread[11] / #37712

    2012/07/12-12:47:28.527 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:47:28.531 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 50

    2012/07/12-12:47:28.534 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-12:47:28.540 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:47:28.543 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 505 -> level: 0

    2012/07/12-12:47:28.549 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 505

    2012/07/12-12:47:28.552 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 582 -> level: 0

    2012/07/12-12:47:28.558 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 582

    2012/07/12-12:47:28.561 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.4 -> level: 0

    2012/07/12-12:47:28.567 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.4

    2012/07/12-12:47:28.570 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1415

    2012/07/12-12:47:28.572 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-12:47:28.578 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:47:28.582 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-12:47:28.584 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097896

    2012/07/12-12:47:28.587 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:47:28.589 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:29.037 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:47:29.393 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:30.337 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:47:31.931 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:31.935 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:34.632 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:34.635 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:34.832 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:47:35.422 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:36.934 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:47:37.037 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:37.041 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:40.734 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:40.737 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:41.531 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:42.134 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:42.138 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:46.831 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:46.834 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:47.036 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:47:47.239 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:47:47.243 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:47.622 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:50.435 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:47:52.339 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:52.343 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:47:52.937 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:52.940 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:53.385 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:47:53.741 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:47:57.134 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:47:57.434 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:47:57.438 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:47:57.440 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:47:59.033 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:47:59.036 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:47:59.485 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:47:59.756 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:47:59.830 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:47:59.854 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:02.537 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:02.541 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:02.544 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:48:04.845 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:48:05.038 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:05.041 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:05.445 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-12:48:05.757 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:48:05.830 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:48:05.853 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:07.236 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:48:07.643 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:07.647 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:10.540 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:48:11.144 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:11.146 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:11.855 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-12:48:11.949 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:12.742 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:12.745 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:17.238 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:17.241 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:17.341 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:48:17.841 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:48:17.845 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:17.945 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:48:18.039 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:22.943 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:22.948 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:23.340 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:23.343 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:24.056 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-12:48:24.150 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:24.153 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:48:24.156 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:48:27.443 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:48:28.042 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:28.046 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:29.212 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:48:29.217 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 49.9

    2012/07/12-12:48:29.220 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:48:29.223 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 507

    2012/07/12-12:48:29.226 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1413

    2012/07/12-12:48:29.230 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342097956

    2012/07/12-12:48:29.439 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:29.442 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:30.208 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:48:30.232 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:30.645 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:48:33.139 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:33.143 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:34.946 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:48:35.449 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:35.452 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:36.218 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:48:36.242 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:37.545 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:48:38.145 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:38.148 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:41.551 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:41.554 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:41.932 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:48:42.001 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2100 -> level: 0

    2012/07/12-12:48:42.007 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2100

    2012/07/12-12:48:42.358 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:43.252 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:43.255 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-12:48:43.258 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1470

    2012/07/12-12:48:47.645 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:48:47.647 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:47.650 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:48:48.021 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:48:48.102 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:48:48.109 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:48:48.348 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:48.352 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:48:48.354 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:48:48.457 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:50.747 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:48:53.452 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:53.456 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:48:53.749 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:53.752 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:48:54.212 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:48:54.484 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:48:54.557 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:48:54.580 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:48:57.753 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:48:58.545 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:48:58.549 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:48:58.552 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:48:59.854 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:48:59.856 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:00.300 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:49:00.657 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:03.651 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:49:03.654 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:49:03.656 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:49:04.961 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:49:05.454 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:49:05.961 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:49:05.964 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:06.411 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:49:06.766 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:07.859 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:49:08.761 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:49:08.765 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:49:08.768 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:49:10.760 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:49:12.054 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:49:12.057 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:12.510 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:49:12.517 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:49:12.782 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:49:12.856 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:49:12.879 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:13.862 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:49:13.865 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:49:13.866 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:49:17.958 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:49:18.160 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:49:18.163 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:18.609 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:49:18.615 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:49:18.881 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:49:18.954 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:49:18.957 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:18.960 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:49:18.956 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:49:18.984 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:24.058 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:49:24.061 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:24.254 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:49:24.257 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:25.045 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:25.049 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:49:25.051 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:49:28.059 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:49:29.160 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:49:29.164 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:30.139 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:49:30.144 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 505

    2012/07/12-12:49:30.146 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 584

    2012/07/12-12:49:30.149 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1415

    2012/07/12-12:49:30.153 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098018

    2012/07/12-12:49:30.357 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:49:30.360 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:30.856 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-12:49:31.165 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:34.260 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:49:34.264 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:35.072 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-12:49:36.365 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:49:36.369 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:37.080 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:49:37.175 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:38.069 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:49:39.371 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:49:39.374 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:42.467 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:49:42.470 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:42.919 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:49:42.926 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:49:43.255 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:49:43.278 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:44.471 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:49:44.475 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:49:44.478 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:49:48.171 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:49:48.572 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:49:48.574 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:49.018 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:49:49.025 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:49:49.290 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:49:49.364 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:49:49.387 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:49.570 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:49:49.573 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:49.576 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:49:50.869 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:49:54.674 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:49:54.678 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:49:54.674 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:49:54.682 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:49:55.473 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:49:58.270 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:49:59.771 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:49:59.775 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:00.767 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:50:00.770 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:01.227 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:50:01.499 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-12:50:01.572 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:50:01.595 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:04.881 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:50:04.885 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:50:04.887 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:50:05.180 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:50:05.473 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:50:06.780 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:50:06.783 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:07.236 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:50:07.509 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:50:07.603 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:08.376 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:50:09.978 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:50:09.982 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:09.985 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:50:10.977 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:50:12.882 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:50:12.884 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:13.326 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:50:13.333 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:50:13.682 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:15.076 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:50:15.080 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:50:15.082 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:50:18.474 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:50:18.976 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:18.979 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:19.426 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:50:19.433 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:50:19.781 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:20.175 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:50:20.179 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:20.182 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:50:25.076 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:25.080 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:25.273 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #42632

    2012/07/12-12:50:25.278 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:25.872 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:25.876 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:50:25.878 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:50:28.576 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:50:30.376 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:50:30.380 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:30.934 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:50:30.940 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 507

    2012/07/12-12:50:30.942 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 582

    2012/07/12-12:50:30.946 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1413

    2012/07/12-12:50:30.950 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098079

    2012/07/12-12:50:31.083 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-12:50:31.176 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:31.179 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:31.886 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-12:50:31.960 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-12:50:31.983 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:35.291 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-12:50:35.384 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:50:35.388 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:37.190 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:37.193 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:37.635 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-12:50:37.906 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:50:37.980 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:50:38.004 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:38.587 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:50:40.490 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:50:40.494 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-12:50:40.496 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-12:50:43.289 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:43.292 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:43.734 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:50:44.081 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:45.585 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:50:45.589 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:45.592 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:50:48.685 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:50:49.385 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:49.388 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:50.159 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:50:50.183 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:50.686 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:50:50.690 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:51.183 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-12:50:55.487 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:50:55.490 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:50:55.793 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:50:55.797 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:50:55.944 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-12:50:56.279 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:50:56.303 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:50:58.786 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:51:00.888 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:00.891 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-12:51:00.894 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-12:51:01.587 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:01.590 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:02.032 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:51:02.378 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:05.391 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-12:51:05.494 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[7] / #39984

    2012/07/12-12:51:05.993 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:05.997 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:51:06.000 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:51:07.592 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:07.595 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:08.388 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:08.791 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:51:11.092 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:11.096 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:51:11.199 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-12:51:13.692 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:13.695 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:14.153 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:51:14.159 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:51:14.508 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:16.201 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:16.205 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:51:16.209 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:51:18.892 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:51:19.792 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:19.795 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:20.241 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:51:20.248 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:51:20.578 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:51:20.601 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:21.295 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:21.299 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:51:21.302 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:51:25.895 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:51:25.898 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:51:26.392 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #25448

    2012/07/12-12:51:26.397 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:51:28.999 | TaskManager      | Run task: 'Flush DB' on thread[10] / #25448

    2012/07/12-12:51:30.959 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:51:30.964 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:51:30.966 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 506

    2012/07/12-12:51:30.969 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 585

    2012/07/12-12:51:30.972 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1414

    2012/07/12-12:51:30.976 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:51:30.978 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098139

    2012/07/12-12:51:30.981 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:30.984 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:31.301 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-12:51:31.429 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:51:31.494 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:51:31.498 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:51:31.701 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 236 -> level: 0

    2012/07/12-12:51:31.708 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:51:31.775 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 237 -> level: 0

    2012/07/12-12:51:31.781 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:51:31.804 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:35.408 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-12:51:36.501 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:36.505 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:51:37.008 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:37.011 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:37.805 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:39.108 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:51:41.601 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:41.605 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:51:43.108 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:51:43.111 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:43.559 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:51:43.566 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:51:43.831 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:51:43.904 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:51:43.927 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:46.709 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-12:51:46.712 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:51:46.715 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:51:49.203 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:51:49.206 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:49.207 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-12:51:49.648 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:51:49.655 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:51:49.920 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-12:51:49.927 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:51:50.014 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:51.408 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:51:51.801 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:51:51.804 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:51:51.807 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:51:55.310 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:51:55.312 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:51:56.019 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 236 -> level: 0

    2012/07/12-12:51:56.026 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:51:56.094 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:51:56.117 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:51:56.910 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:51:56.913 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:51:59.306 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:52:01.409 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:01.412 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:01.797 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:52:01.877 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:52:02.009 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:52:02.011 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:02.013 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:52:02.149 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:52:02.223 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:52:02.245 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:05.508 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:52:05.521 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:52:07.116 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:07.120 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:07.513 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:07.516 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:07.887 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:52:08.229 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:52:08.303 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:52:08.326 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:09.409 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:52:11.509 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:52:12.212 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:12.216 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:13.609 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:13.612 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:14.383 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 238

    2012/07/12-12:52:14.406 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:17.309 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:17.313 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:19.515 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:52:19.715 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:19.717 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:20.512 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:22.415 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:22.419 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:25.812 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:25.815 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:26.602 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:26.606 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:52:26.608 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:52:27.516 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:27.520 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:29.616 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:52:31.619 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:52:31.685 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:52:31.689 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 50

    2012/07/12-12:52:31.692 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 588 -> level: 0

    2012/07/12-12:52:31.698 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 588

    2012/07/12-12:52:31.704 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098200

    2012/07/12-12:52:31.912 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:31.915 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:32.295 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:52:32.365 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:52:32.617 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:52:32.621 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:52:32.625 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:52:32.627 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 237

    2012/07/12-12:52:32.721 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:35.515 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:52:37.718 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:37.722 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:52:38.024 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:38.027 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:38.405 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:52:38.485 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:52:38.757 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:52:38.851 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:39.724 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:52:42.826 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:42.830 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:52:42.833 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:52:44.125 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:44.128 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:44.901 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:52:44.924 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:47.917 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:47.921 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:52:49.823 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:52:50.224 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:50.227 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:50.674 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:52:51.001 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 238

    2012/07/12-12:52:51.024 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:51.717 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:52:53.021 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:53.025 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:53.028 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:52:56.321 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:52:56.323 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:52:57.026 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 238 -> level: 0

    2012/07/12-12:52:57.033 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 238

    2012/07/12-12:52:57.100 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 239 -> level: 0

    2012/07/12-12:52:57.106 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 239

    2012/07/12-12:52:57.129 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:52:58.121 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:52:58.126 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:52:59.918 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:53:02.421 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:02.424 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:02.884 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:53:02.891 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:53:03.157 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 237

    2012/07/12-12:53:03.222 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:53:03.225 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:53:03.228 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:53:03.231 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 238

    2012/07/12-12:53:03.253 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:05.526 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:53:05.533 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-12:53:08.229 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:08.232 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:53:08.425 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:08.428 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:08.873 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:53:08.880 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:53:09.145 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 238

    2012/07/12-12:53:09.220 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 239

    2012/07/12-12:53:09.243 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:09.926 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:53:11.729 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:53:13.334 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:13.338 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:13.341 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:53:14.533 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:14.536 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:15.245 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 237

    2012/07/12-12:53:15.339 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:18.432 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:18.434 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:20.026 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:53:20.635 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:20.638 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:21.092 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:53:21.438 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:23.532 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:23.535 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:53:23.537 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:53:26.629 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-12:53:26.633 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:53:28.626 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #35036

    2012/07/12-12:53:28.630 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:53:30.133 | TaskManager      | Run task: 'Flush DB' on thread[10] / #35036

    2012/07/12-12:53:31.689 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:53:31.693 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 49.9

    2012/07/12-12:53:31.697 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 517 -> level: 0

    2012/07/12-12:53:31.702 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 517

    2012/07/12-12:53:31.705 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 590

    2012/07/12-12:53:31.708 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1403

    2012/07/12-12:53:31.712 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:53:31.717 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:53:31.720 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098259

    2012/07/12-12:53:31.722 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:53:31.724 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:31.832 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:53:32.110 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:53:32.190 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:53:32.197 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:53:32.525 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 238

    2012/07/12-12:53:32.548 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:33.736 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:33.740 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:33.743 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:53:35.535 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:53:37.737 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:37.739 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:38.120 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:53:38.546 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:38.840 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:38.844 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:40.237 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:53:43.842 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:43.844 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:43.944 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:53:43.948 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:44.635 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:49.038 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:49.042 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:49.935 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:49.938 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:50.341 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:53:50.399 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:53:50.671 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 236 -> level: 0

    2012/07/12-12:53:50.677 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:53:50.764 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:51.837 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:53:54.141 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:54.144 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:53:54.147 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:53:56.039 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:53:56.041 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:53:56.489 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:53:56.825 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 237 -> level: 0

    2012/07/12-12:53:56.831 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:53:56.854 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:53:59.236 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:53:59.240 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:53:59.242 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:54:00.435 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:54:02.140 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:02.143 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:02.588 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:54:02.595 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:54:02.944 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:04.338 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:04.342 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:54:04.345 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:54:05.552 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-12:54:05.552 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:54:08.245 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:08.248 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:08.708 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:54:08.714 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:54:09.064 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:09.347 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:09.351 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:54:09.354 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:54:10.446 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:54:11.850 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:54:14.345 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:14.348 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:14.445 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:54:14.448 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:54:14.807 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:54:15.069 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:54:15.144 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:54:15.167 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:19.550 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:19.553 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:54:19.556 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:54:20.448 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:20.451 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:20.551 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:54:21.252 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:24.647 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:24.651 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:54:26.554 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:26.557 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:27.353 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:27.356 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:54:27.358 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:54:29.746 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:29.750 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:54:30.653 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:54:31.946 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:54:32.425 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:54:32.430 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-12:54:32.436 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:54:32.439 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 511 -> level: 0

    2012/07/12-12:54:32.445 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 511

    2012/07/12-12:54:32.447 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 586

    2012/07/12-12:54:32.450 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1409

    2012/07/12-12:54:32.452 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-12:54:32.458 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:54:32.462 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:54:32.464 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098320

    2012/07/12-12:54:32.650 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:32.653 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:33.096 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:54:33.358 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:54:33.433 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:54:33.456 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:34.759 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:34.763 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:54:35.656 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:54:38.758 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:38.761 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:39.216 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:54:39.488 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:54:39.561 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:54:39.584 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:39.856 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:39.860 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:54:39.862 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:54:40.755 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:54:44.852 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:44.855 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:44.960 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:54:44.963 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:54:45.558 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:54:45.632 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:54:45.655 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:50.058 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:50.062 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:54:50.855 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:54:50.956 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:50.959 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:51.405 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:54:51.751 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:54:51.954 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:54:55.159 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:54:55.164 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:54:55.166 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:54:57.059 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:54:57.061 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:54:57.861 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:00.255 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:00.259 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:00.961 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:55:03.160 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:03.162 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:03.535 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:55:03.615 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:55:03.622 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:55:03.951 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 237 -> level: 0

    2012/07/12-12:55:03.958 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:55:03.981 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:05.269 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:05.272 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:55:05.275 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:55:05.567 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:55:05.669 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:55:09.266 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:09.268 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:09.644 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:55:09.714 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:55:10.059 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:10.362 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:10.365 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:10.368 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:55:11.060 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:55:11.959 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:55:15.363 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:15.365 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:15.463 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:55:15.466 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:16.076 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 236 -> level: 0

    2012/07/12-12:55:16.083 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:55:16.170 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:20.563 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:20.567 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:21.170 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:55:21.470 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:21.472 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:21.843 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:55:22.185 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:55:22.259 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:55:22.283 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:25.667 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:25.671 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:27.364 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-12:55:27.367 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:55:30.762 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #40668

    2012/07/12-12:55:30.767 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:31.270 | TaskManager      | Run task: 'Flush DB' on thread[10] / #40668

    2012/07/12-12:55:31.970 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #40668

    2012/07/12-12:55:32.430 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:55:32.435 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 507

    2012/07/12-12:55:32.438 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 585

    2012/07/12-12:55:32.441 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1413

    2012/07/12-12:55:32.444 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:55:32.447 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:55:32.450 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:55:32.456 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:55:32.459 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098380

    2012/07/12-12:55:32.462 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:55:32.464 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:32.911 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:55:33.183 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:55:33.277 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:35.771 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:55:35.779 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:35.783 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:38.474 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:38.477 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:38.919 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:55:39.274 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:40.867 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:40.871 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:55:40.873 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:55:41.376 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:55:44.569 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:44.572 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:45.277 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:55:45.352 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:55:45.375 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:45.968 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:45.972 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:55:50.673 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:50.676 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:51.069 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:55:51.073 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:55:51.122 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:55:51.394 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:55:51.465 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:55:51.468 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:55:51.491 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:55:52.064 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:55:56.167 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:55:56.171 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:55:56.174 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:55:56.766 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:55:56.768 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:55:57.211 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:55:57.483 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:55:57.577 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:01.270 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:01.274 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:56:01.277 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:56:01.569 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:56:02.870 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:02.873 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:03.320 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:56:03.327 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:56:03.676 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:05.879 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:56:06.072 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:56:06.372 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:06.376 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:56:06.379 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:56:08.971 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:08.974 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:09.419 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:56:09.775 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:11.478 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:11.482 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:56:11.485 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:56:11.677 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:56:12.077 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:56:15.070 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:15.073 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:15.854 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:56:15.878 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:16.571 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:16.575 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:56:21.177 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:21.180 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:21.627 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:56:21.634 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:56:21.679 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:56:21.682 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:56:21.685 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:56:21.777 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:56:21.983 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:26.777 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:26.781 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:56:27.274 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:27.277 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:28.072 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:28.075 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:56:28.078 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:56:31.876 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:31.879 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:56:31.880 | TaskManager      | Run task: 'Flush DB' on thread[10] / #40668

    2012/07/12-12:56:32.171 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:56:33.156 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:56:33.161 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 510

    2012/07/12-12:56:33.164 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 584

    2012/07/12-12:56:33.167 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1410

    2012/07/12-12:56:33.170 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:56:33.174 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:56:33.176 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098441

    2012/07/12-12:56:33.374 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:33.376 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:33.757 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:56:34.183 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:35.986 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:56:36.979 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:36.983 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:56:36.986 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:56:39.378 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:39.381 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:39.826 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:56:40.153 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:56:40.176 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:41.979 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:56:42.082 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:42.085 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:56:42.088 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:56:45.480 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:45.483 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:45.926 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:56:46.197 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:56:46.271 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 238

    2012/07/12-12:56:46.294 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:47.186 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:47.190 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:56:47.193 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:56:51.586 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:51.589 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:51.966 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:56:52.045 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:56:52.051 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:56:52.082 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:56:52.183 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-12:56:52.286 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:56:52.289 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:56:52.292 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:56:52.318 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 237

    2012/07/12-12:56:52.412 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:56:57.385 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:56:57.389 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:56:57.681 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:56:57.684 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:56:58.064 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:56:58.144 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:56:58.151 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:56:58.416 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:56:58.490 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:56:58.513 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:02.187 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:57:02.488 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:02.492 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:57:02.494 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:57:03.787 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:03.790 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:04.235 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:57:04.590 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:06.094 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:57:06.096 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:57:07.594 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:07.598 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:57:07.600 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:57:09.892 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:09.895 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:10.344 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-12:57:10.351 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:57:10.616 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:57:10.711 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:12.193 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:57:12.296 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:57:12.690 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:12.694 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:57:12.696 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:57:15.989 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:15.992 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:16.433 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:57:16.769 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:57:16.793 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:17.796 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:17.800 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:57:17.803 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:57:22.096 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:22.098 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:22.390 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:57:22.554 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2100 -> level: 0

    2012/07/12-12:57:22.561 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2100

    2012/07/12-12:57:22.826 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:57:22.890 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:57:22.894 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-12:57:22.896 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1470

    2012/07/12-12:57:22.899 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:57:22.921 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:27.993 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:27.997 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-12:57:28.089 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-12:57:28.092 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:57:32.289 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #29468

    2012/07/12-12:57:32.492 | TaskManager      | Run task: 'Flush DB' on thread[10] / #29468

    2012/07/12-12:57:33.093 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #29468

    2012/07/12-12:57:33.097 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-12:57:33.150 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:57:33.155 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 586

    2012/07/12-12:57:33.160 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:57:33.163 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:57:33.166 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098501

    2012/07/12-12:57:33.168 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-12:57:33.171 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:33.561 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:57:33.641 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:57:33.647 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:57:33.912 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:57:33.986 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:57:34.010 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:36.198 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:57:38.201 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:38.204 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:57:38.207 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:57:39.199 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:39.202 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:40.007 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:42.600 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:57:43.303 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:43.307 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:57:45.299 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:45.302 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:46.096 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:48.399 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:48.404 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:57:51.398 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:51.401 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:51.860 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:57:51.867 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:57:52.215 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:52.298 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:57:52.701 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:57:53.501 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:53.505 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:57:53.508 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:57:57.500 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:57:57.502 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:57:57.949 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:57:57.956 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:57:58.305 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:57:58.598 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:57:58.601 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:57:58.604 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:58:02.797 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:58:03.597 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:03.600 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:03.697 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:58:03.700 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:04.049 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:58:04.310 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 236

    2012/07/12-12:58:04.385 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:58:04.407 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:06.112 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:58:06.212 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-12:58:08.704 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:08.708 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:58:08.711 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:58:09.604 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:09.606 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:10.059 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:58:10.330 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-12:58:10.337 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:58:10.404 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:58:10.427 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:12.310 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:58:12.813 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:58:13.805 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:13.809 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:13.812 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:58:15.705 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:15.707 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:16.420 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-12:58:16.514 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:18.906 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:18.909 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:21.813 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:21.816 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:22.258 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2100 -> level: 0

    2012/07/12-12:58:22.266 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2100

    2012/07/12-12:58:22.614 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:22.907 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:58:24.006 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:24.010 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-12:58:24.012 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1470

    2012/07/12-12:58:27.905 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:27.908 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:28.367 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-12:58:28.374 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:58:28.722 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:28.724 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:58:28.727 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:58:29.114 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:29.118 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:29.121 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:58:32.414 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:58:33.007 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:58:33.807 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:58:33.812 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 518 -> level: 0

    2012/07/12-12:58:33.819 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 518

    2012/07/12-12:58:33.821 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 589

    2012/07/12-12:58:33.824 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1402

    2012/07/12-12:58:33.828 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098561

    2012/07/12-12:58:34.012 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:34.015 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:34.211 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:58:34.216 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:34.803 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:36.316 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:58:39.319 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:39.322 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:40.116 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:40.119 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:40.912 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:43.015 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:58:44.417 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:44.420 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:58:46.213 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:46.216 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:46.676 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-12:58:47.012 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 237

    2012/07/12-12:58:47.035 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:49.518 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:49.521 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-12:58:49.523 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-12:58:52.316 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:52.319 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:52.521 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-12:58:52.695 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:58:52.765 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:58:52.769 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:58:53.102 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-12:58:53.113 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:58:53.125 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:54.617 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:54.621 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:58:54.623 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:58:58.416 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:58:58.418 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:58:58.795 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:58:58.865 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:58:58.871 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:58:59.220 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:58:59.713 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:58:59.717 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:58:59.719 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:59:03.214 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:59:04.516 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:04.519 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:04.729 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:59:04.732 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:59:04.905 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:59:04.985 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-12:59:05.341 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:06.123 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-12:59:06.322 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:59:09.825 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:09.829 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-12:59:09.831 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-12:59:10.525 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:10.528 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:10.905 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:59:10.984 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-12:59:11.247 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-12:59:11.253 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-12:59:11.321 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-12:59:11.327 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-12:59:11.350 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:12.623 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-12:59:13.226 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:59:14.921 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:14.925 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-12:59:14.927 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-12:59:16.629 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:16.632 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:17.004 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-12:59:17.074 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:59:17.080 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:59:17.429 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:20.023 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:20.028 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:59:20.031 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:59:22.723 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:22.725 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:23.325 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-12:59:23.436 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-12:59:23.530 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:25.123 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:25.127 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:59:28.826 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-12:59:28.828 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-12:59:30.222 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #48148

    2012/07/12-12:59:30.225 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:59:32.728 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #48148

    2012/07/12-12:59:33.431 | TaskManager      | Run task: 'Flush DB' on thread[10] / #48148

    2012/07/12-12:59:33.881 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-12:59:33.886 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-12:59:33.892 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:59:33.895 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 531 -> level: 0

    2012/07/12-12:59:33.901 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 531

    2012/07/12-12:59:33.903 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 606 -> level: 0

    2012/07/12-12:59:33.912 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 606

    2012/07/12-12:59:33.915 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.5 -> level: 0

    2012/07/12-12:59:33.924 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.5

    2012/07/12-12:59:33.928 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1389

    2012/07/12-12:59:33.931 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-12:59:33.937 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:59:33.940 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-12:59:33.943 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098622

    2012/07/12-12:59:33.946 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:33.948 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:34.392 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:59:34.398 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:59:34.747 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:35.240 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:35.244 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:59:35.247 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-12:59:36.339 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-12:59:40.033 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:40.036 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:40.341 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-12:59:40.345 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:59:40.827 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:43.541 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:59:45.434 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:45.438 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-12:59:46.140 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:46.143 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:46.590 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 1950 -> level: 0

    2012/07/12-12:59:46.597 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 1950

    2012/07/12-12:59:46.863 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-12:59:46.957 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:50.541 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:50.545 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-12:59:50.547 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1365

    2012/07/12-12:59:52.240 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-12:59:52.243 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:52.690 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-12:59:52.697 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-12:59:52.739 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-12:59:52.962 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 231 -> level: 0

    2012/07/12-12:59:52.969 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-12:59:53.036 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 232 -> level: 0

    2012/07/12-12:59:53.042 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-12:59:53.065 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-12:59:53.637 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-12:59:55.640 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-12:59:55.645 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-12:59:55.647 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-12:59:58.340 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-12:59:58.344 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-12:59:58.800 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-12:59:58.806 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-12:59:59.072 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-12:59:59.078 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-12:59:59.145 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-12:59:59.152 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-12:59:59.175 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:00.738 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:00.742 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:00:00.745 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:00:03.738 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:00:04.436 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:04.438 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:04.879 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2100 -> level: 0

    2012/07/12-13:00:04.885 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2100

    2012/07/12-13:00:05.236 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:05.849 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:05.852 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-13:00:05.855 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1470

    2012/07/12-13:00:06.147 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[7] / #39984

    2012/07/12-13:00:06.449 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-13:00:10.444 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:10.448 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:10.890 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-13:00:10.897 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:00:10.951 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:00:10.955 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:00:10.958 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:00:11.245 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:12.749 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-13:00:13.743 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:00:16.045 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:16.049 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:00:16.542 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:16.544 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:16.999 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:00:17.334 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:00:17.357 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:21.151 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:21.155 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:00:21.158 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:00:22.650 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:22.652 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:23.028 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-13:00:23.361 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:00:23.455 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:23.848 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:00:26.187 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:26.191 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:00:28.684 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:28.686 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:29.473 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:29.476 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-13:00:29.478 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:00:31.287 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:31.290 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:00:32.883 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-13:00:33.990 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:00:34.547 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:00:34.552 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 516 -> level: 0

    2012/07/12-13:00:34.558 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 516

    2012/07/12-13:00:34.560 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 595 -> level: 0

    2012/07/12-13:00:34.567 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 595

    2012/07/12-13:00:34.571 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1404

    2012/07/12-13:00:34.576 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-13:00:34.583 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-13:00:34.586 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098683

    2012/07/12-13:00:34.786 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:34.789 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:35.178 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:00:35.593 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:36.386 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:36.389 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-13:00:36.391 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-13:00:36.483 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-13:00:40.886 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:40.889 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:41.267 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-13:00:41.337 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:00:41.489 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:00:41.492 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:00:41.494 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:00:41.684 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:44.087 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:00:46.591 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:46.594 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:00:46.986 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:46.989 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:47.367 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:00:47.447 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-13:00:47.453 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:00:47.718 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:00:47.792 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:00:47.815 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:51.688 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:51.692 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:00:51.695 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:00:52.988 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-13:00:53.091 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:53.094 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:53.537 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:00:53.892 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:00:54.185 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:00:56.785 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:00:56.788 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:00:56.791 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:00:59.193 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:00:59.196 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:00:59.983 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:01.886 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:01.889 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:01:04.291 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:01:05.288 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:05.291 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:05.736 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-13:01:05.742 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-13:01:06.091 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:06.163 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[7] / #39984

    2012/07/12-13:01:06.587 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-13:01:06.990 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:06.994 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-13:01:06.996 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-13:01:11.390 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:11.392 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:11.776 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-13:01:11.855 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:01:12.089 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:01:12.092 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:01:12.094 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:01:12.202 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:13.094 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-13:01:14.387 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:01:17.187 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:17.190 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:01:17.492 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:17.495 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:17.864 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:01:17.935 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-13:01:17.941 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:01:18.206 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-13:01:18.212 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:01:18.280 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-13:01:18.286 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:01:18.308 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:22.292 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:22.295 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:01:22.297 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:01:23.590 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:23.592 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:24.045 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:01:24.400 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:24.493 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:01:27.393 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:27.396 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:01:27.399 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:01:29.492 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[7] / #39984

    2012/07/12-13:01:29.494 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:01:32.487 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #31152

    2012/07/12-13:01:32.491 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:01:33.193 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #31152

    2012/07/12-13:01:34.531 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:01:34.536 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 50

    2012/07/12-13:01:34.538 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 235 -> level: 0

    2012/07/12-13:01:34.544 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:01:34.546 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 513

    2012/07/12-13:01:34.549 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 588 -> level: 0

    2012/07/12-13:01:34.554 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 588

    2012/07/12-13:01:34.556 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.4 -> level: 0

    2012/07/12-13:01:34.562 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.4

    2012/07/12-13:01:34.564 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Frequency' = 50

    2012/07/12-13:01:34.567 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1407

    2012/07/12-13:01:34.569 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 236 -> level: 0

    2012/07/12-13:01:34.574 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:01:34.578 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:01:34.581 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098743

    2012/07/12-13:01:34.583 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:01:34.585 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:34.593 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:01:35.303 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:01:35.378 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:01:35.400 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:36.689 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-13:01:37.592 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:37.595 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:01:37.598 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:01:40.591 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:40.594 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:41.397 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:42.690 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:42.694 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:01:44.697 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:01:46.697 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:46.699 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:47.467 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:01:47.490 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:47.793 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:47.797 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:01:52.790 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:52.793 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:52.894 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:01:52.897 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:01:53.290 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-13:01:53.567 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:01:53.590 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:01:54.793 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:01:57.992 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:01:57.996 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:01:58.899 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:01:58.903 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:01:59.290 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 29

    2012/07/12-13:01:59.370 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 1950 -> level: 0

    2012/07/12-13:01:59.377 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 1950

    2012/07/12-13:01:59.642 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 231 -> level: 0

    2012/07/12-13:01:59.649 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:01:59.716 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 232 -> level: 0

    2012/07/12-13:01:59.723 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-13:01:59.746 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:03.097 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:03.101 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-13:02:03.103 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1365

    2012/07/12-13:02:04.898 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:02:04.992 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:04.995 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:05.370 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:02:05.449 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-13:02:05.456 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:02:05.722 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-13:02:05.728 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:02:05.796 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-13:02:05.803 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:02:05.825 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:06.188 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-13:02:06.796 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:02:08.199 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:08.203 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:02:08.206 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:02:11.099 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:11.102 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:11.811 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 231 -> level: 0

    2012/07/12-13:02:11.818 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:02:11.886 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 232 -> level: 0

    2012/07/12-13:02:11.893 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-13:02:11.915 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:13.298 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:13.301 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:02:13.394 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:02:14.997 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:02:17.201 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:17.203 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:17.649 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:02:17.911 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:02:17.985 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:02:18.008 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:18.400 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:18.404 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:02:18.406 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:02:23.300 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:23.303 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:23.500 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:02:23.504 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:02:23.749 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-13:02:24.021 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-13:02:24.029 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:02:24.095 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 236 -> level: 0

    2012/07/12-13:02:24.101 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:02:24.123 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:25.096 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:02:28.598 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:28.601 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:02:28.604 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-13:02:29.396 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:29.399 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:29.848 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:02:30.121 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:02:30.214 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:30.217 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-13:02:30.220 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:02:33.498 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:02:33.701 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:33.705 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:02:33.707 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:02:35.200 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:02:35.288 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:02:35.293 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-13:02:35.299 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:02:35.302 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 503 -> level: 0

    2012/07/12-13:02:35.309 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 503

    2012/07/12-13:02:35.312 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 577 -> level: 0

    2012/07/12-13:02:35.318 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 577

    2012/07/12-13:02:35.321 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1417

    2012/07/12-13:02:35.324 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-13:02:35.330 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:02:35.334 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-13:02:35.337 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098803

    2012/07/12-13:02:35.501 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:35.504 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:36.274 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:02:36.297 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:36.900 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:02:38.803 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:38.807 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:02:38.809 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-13:02:41.602 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:41.605 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:41.979 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-13:02:42.058 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:02:42.320 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 235 -> level: 0

    2012/07/12-13:02:42.326 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:02:42.394 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 236 -> level: 0

    2012/07/12-13:02:42.400 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:02:42.422 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:43.895 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:43.899 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:02:43.902 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:02:45.304 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:02:47.696 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:47.699 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:48.087 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:02:48.167 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-13:02:48.439 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:02:48.533 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:48.996 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:48.999 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:02:49.002 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-13:02:53.605 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:02:53.798 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:53.801 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:02:54.102 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:02:54.106 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:02:54.247 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:02:54.583 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:02:54.607 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:02:55.399 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:02:59.200 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:02:59.203 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:02:59.207 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:02:59.900 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:02:59.903 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:00.608 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 233 -> level: 0

    2012/07/12-13:03:00.616 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:03:00.683 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 234 -> level: 0

    2012/07/12-13:03:00.689 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:03:00.712 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:04.305 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:04.309 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:05.505 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:03:06.006 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:06.009 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:06.205 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[9] / #38128

    2012/07/12-13:03:06.718 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:03:06.792 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:03:06.815 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:06.998 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:03:09.400 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:09.403 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:12.106 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:12.109 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:12.557 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-13:03:12.564 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-13:03:12.828 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:03:12.922 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:13.705 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:03:14.498 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:14.502 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-13:03:14.504 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-13:03:15.606 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:03:18.200 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:18.203 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:18.645 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-13:03:18.651 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:03:18.917 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:03:19.012 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:19.605 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:19.609 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:19.612 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:03:24.306 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:24.309 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:24.702 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:03:24.706 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:24.755 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:03:25.111 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:25.704 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:03:29.806 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:29.810 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:03:29.813 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:03:30.306 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-13:03:30.309 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:03:33.799 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #43656

    2012/07/12-13:03:34.914 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #43656

    2012/07/12-13:03:34.918 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:03:35.372 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:03:35.376 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 49.9

    2012/07/12-13:03:35.380 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:03:35.382 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 505

    2012/07/12-13:03:35.385 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 579

    2012/07/12-13:03:35.388 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1415

    2012/07/12-13:03:35.390 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:03:35.394 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:03:35.396 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098863

    2012/07/12-13:03:35.399 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:03:35.401 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:35.809 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:03:36.189 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:37.012 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:03:40.006 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:40.010 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:40.013 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:03:41.406 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:41.409 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:42.114 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 230 -> level: 0

    2012/07/12-13:03:42.121 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 230

    2012/07/12-13:03:42.188 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 231 -> level: 0

    2012/07/12-13:03:42.195 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 231

    2012/07/12-13:03:42.217 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:45.110 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:45.114 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:45.906 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:03:47.509 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:47.512 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:48.234 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 233 -> level: 0

    2012/07/12-13:03:48.240 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:03:48.307 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 234 -> level: 0

    2012/07/12-13:03:48.314 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:03:48.337 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:50.210 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:50.214 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:53.607 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:53.610 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:03:53.815 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-13:03:54.378 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:03:54.401 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:03:55.314 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:03:55.318 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:03:56.010 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:03:59.708 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:03:59.711 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:00.410 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:04:00.414 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:00.423 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:04:00.517 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:04.212 | TaskManager      | Run task: 'Purge Log' on thread:emotion-29: / #6740

    2012/07/12-13:04:05.416 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:05.420 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:05.722 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:05.724 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:06.024 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-13:04:06.224 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[10] / #43656

    2012/07/12-13:04:06.443 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:04:06.536 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:07.120 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:04:10.524 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:10.528 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:11.820 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:11.823 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:12.532 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:04:12.626 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:13.919 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:04:15.623 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:15.627 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:16.119 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:04:17.919 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:17.922 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:18.631 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:04:18.705 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:04:18.728 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:20.722 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:20.726 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:24.019 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:24.022 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:24.795 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:04:24.819 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:25.822 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:25.826 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:26.219 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:04:30.120 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:30.123 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:30.896 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:04:30.919 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:30.922 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-13:04:30.925 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:04:30.926 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #43656

    2012/07/12-13:04:30.928 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:34.022 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:04:35.988 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:04:35.993 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 50

    2012/07/12-13:04:35.996 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:04:35.999 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 506

    2012/07/12-13:04:36.002 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 575

    2012/07/12-13:04:36.005 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Frequency' = 49.9

    2012/07/12-13:04:36.007 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1414

    2012/07/12-13:04:36.010 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 232 -> level: 0

    2012/07/12-13:04:36.016 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-13:04:36.019 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 29

    2012/07/12-13:04:36.023 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 1950 -> level: 0

    2012/07/12-13:04:36.029 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 1950

    2012/07/12-13:04:36.031 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098924

    2012/07/12-13:04:36.033 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:36.035 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-13:04:36.037 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1365

    2012/07/12-13:04:36.129 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:36.132 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:36.225 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-13:04:36.579 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-13:04:36.586 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:04:36.850 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 231 -> level: 0

    2012/07/12-13:04:36.857 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:04:36.944 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:37.128 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:04:41.132 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:41.136 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:04:41.138 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:04:42.231 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:42.234 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:42.619 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:04:42.698 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-13:04:42.704 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:04:42.971 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 233 -> level: 0

    2012/07/12-13:04:42.978 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:04:43.045 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 234 -> level: 0

    2012/07/12-13:04:43.052 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:04:43.074 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:46.227 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:46.231 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:04:46.234 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:04:46.326 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:04:48.327 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:48.329 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:48.707 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 29

    2012/07/12-13:04:48.777 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 1950 -> level: 0

    2012/07/12-13:04:48.783 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 1950

    2012/07/12-13:04:49.049 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 230 -> level: 0

    2012/07/12-13:04:49.056 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 230

    2012/07/12-13:04:49.123 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 231 -> level: 0

    2012/07/12-13:04:49.130 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 231

    2012/07/12-13:04:49.153 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:51.327 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:51.332 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-13:04:51.335 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1365

    2012/07/12-13:04:54.127 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:04:54.430 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:04:54.433 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:04:54.808 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:04:54.888 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-13:04:54.894 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:04:55.159 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-13:04:55.166 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:04:55.233 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-13:04:55.240 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:04:55.263 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:04:56.426 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:04:56.430 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:04:56.432 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:04:56.433 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-13:05:00.536 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:00.539 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:00.987 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:05:01.250 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:05:01.324 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:05:01.347 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:01.529 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:01.532 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:05:01.534 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:05:06.244 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-13:05:06.440 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:05:06.541 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:06.544 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:05:06.637 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:06.640 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:07.086 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:05:07.136 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-13:05:07.348 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:05:07.422 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:05:07.445 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:11.638 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:11.641 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:05:11.644 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:05:12.736 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:12.739 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:13.197 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2130 -> level: 0

    2012/07/12-13:05:13.203 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2130

    2012/07/12-13:05:13.469 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:05:13.542 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-13:05:13.549 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:05:13.571 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:14.144 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:05:16.538 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:05:16.741 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:16.745 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-13:05:16.748 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1491

    2012/07/12-13:05:18.841 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:18.843 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:19.547 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-13:05:19.555 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:05:19.642 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:21.846 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:21.850 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1491 s

    2012/07/12-13:05:24.942 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:24.945 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:25.386 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:05:25.647 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:05:25.741 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:26.644 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:05:26.945 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:26.949 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:05:26.952 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:05:30.945 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-13:05:31.853 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:05:31.967 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #35548

    2012/07/12-13:05:31.970 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:05:34.169 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #35548

    2012/07/12-13:05:36.672 | TaskManager      | Run task: 'Flush DB' on thread[10] / #35548

    2012/07/12-13:05:36.915 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:05:36.919 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:05:36.922 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 516 -> level: 0

    2012/07/12-13:05:36.927 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 516

    2012/07/12-13:05:36.930 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 593 -> level: 0

    2012/07/12-13:05:36.936 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 593

    2012/07/12-13:05:36.938 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.5 -> level: 0

    2012/07/12-13:05:36.944 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.5

    2012/07/12-13:05:36.947 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1404

    2012/07/12-13:05:36.951 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342098985

    2012/07/12-13:05:36.954 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:05:36.957 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:37.074 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:37.078 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:05:37.171 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:05:37.345 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 31

    2012/07/12-13:05:37.771 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:42.174 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:42.178 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:05:42.970 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:42.973 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:43.344 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:05:43.424 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2100

    2012/07/12-13:05:43.696 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-13:05:43.701 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:05:43.770 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-13:05:43.775 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:05:43.797 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:46.769 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:05:47.270 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:47.274 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1470 s

    2012/07/12-13:05:47.277 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1470

    2012/07/12-13:05:49.070 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:49.073 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:49.514 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:05:49.775 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-13:05:49.781 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:05:49.849 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-13:05:49.855 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:05:49.878 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:52.370 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:52.373 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:05:52.376 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:05:54.278 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:05:55.171 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:05:55.174 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:05:55.623 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-13:05:55.630 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:05:55.895 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 231 -> level: 0

    2012/07/12-13:05:55.902 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:05:55.970 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 232 -> level: 0

    2012/07/12-13:05:55.976 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-13:05:55.999 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:05:56.872 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:05:57.476 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:05:57.480 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:05:57.483 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:06:01.277 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:01.280 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:01.734 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:06:02.005 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-13:06:02.011 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:06:02.079 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-13:06:02.086 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:06:02.108 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:02.571 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:02.574 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:06:02.577 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:06:06.375 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-13:06:06.977 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:06:07.279 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:06:07.372 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:07.375 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:07.675 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:06:07.679 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:06:07.833 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:06:08.188 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:12.773 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:12.777 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:06:12.779 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:06:13.472 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:13.474 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:13.922 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:06:14.279 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:14.372 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:06:17.074 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:06:17.872 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:17.876 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:06:17.879 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:06:19.581 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:19.584 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:20.033 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:06:20.388 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:22.981 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:22.984 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:06:22.987 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:06:25.679 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:25.682 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:26.141 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2250 -> level: 0

    2012/07/12-13:06:26.149 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-13:06:26.414 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:06:26.488 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:06:26.510 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:27.173 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:06:28.075 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:28.079 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:06:28.081 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-13:06:31.775 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:31.778 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:32.221 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:06:32.568 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:32.571 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-13:06:32.574 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:06:33.181 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:33.185 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:06:33.188 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:06:34.481 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:06:37.279 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:06:37.378 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:06:37.640 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:06:37.645 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 49.9

    2012/07/12-13:06:37.648 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.ActivePower == 505 -> level: 0

    2012/07/12-13:06:37.654 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 505

    2012/07/12-13:06:37.657 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 583 -> level: 0

    2012/07/12-13:06:37.662 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 583

    2012/07/12-13:06:37.665 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Current == 2.4 -> level: 0

    2012/07/12-13:06:37.671 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Current' = 2.4

    2012/07/12-13:06:37.674 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1415

    2012/07/12-13:06:37.678 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-13:06:37.680 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342099045

    2012/07/12-13:06:37.881 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:37.884 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:38.283 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:06:38.287 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:06:38.289 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-13:06:38.676 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:43.380 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:43.384 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:06:43.976 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:43.979 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:44.430 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:06:44.693 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:06:44.767 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:06:44.790 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:47.383 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:06:48.478 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:48.481 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:06:48.484 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:06:50.077 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:50.080 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:50.782 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:06:50.857 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:06:50.879 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:53.582 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:53.584 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:06:54.576 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:06:56.178 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:06:56.181 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:06:56.891 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:06:56.985 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:06:57.478 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:06:58.679 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:06:58.683 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:02.286 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:02.289 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:02.739 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2190 -> level: 0

    2012/07/12-13:07:02.746 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:07:03.012 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:07:03.086 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:07:03.108 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:03.781 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:03.785 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:07:03.788 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:07:06.883 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-13:07:07.478 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:07:07.581 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:07:08.383 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:08.386 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:08.829 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:07:08.886 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:07:08.890 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:08.893 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:07:09.100 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:07:09.174 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:07:09.198 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:13.982 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:13.986 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:14.479 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:14.482 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:14.687 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-13:07:15.190 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:07:15.264 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:07:15.287 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:17.680 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:07:19.081 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:19.084 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:20.588 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:20.591 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:21.039 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:07:21.311 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:07:21.385 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:07:21.408 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:24.181 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:24.184 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:07:24.187 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:07:26.680 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:26.682 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:27.128 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:07:27.473 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:27.787 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:07:29.286 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:29.290 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:29.292 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:07:32.586 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-13:07:32.589 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:07:34.379 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #30944

    2012/07/12-13:07:34.383 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:34.792 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #30944

    2012/07/12-13:07:37.485 | TaskManager      | Run task: 'Purge Event List' on thread[10] / #30944

    2012/07/12-13:07:37.635 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:07:37.640 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 508

    2012/07/12-13:07:37.642 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Frequency' = 50

    2012/07/12-13:07:37.645 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1412

    2012/07/12-13:07:37.648 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 236

    2012/07/12-13:07:37.651 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342099105

    2012/07/12-13:07:37.654 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:07:37.657 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:37.884 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:07:38.367 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 235

    2012/07/12-13:07:38.461 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:39.386 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:39.390 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:43.693 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:43.695 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:44.135 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:07:44.406 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:07:44.480 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:07:44.485 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:07:44.488 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:07:44.490 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:07:44.504 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:47.987 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:07:49.588 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:49.592 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:07:49.785 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:49.788 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:50.235 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:07:50.507 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 232 -> level: 0

    2012/07/12-13:07:50.514 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:07:50.581 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 233 -> level: 0

    2012/07/12-13:07:50.588 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:07:50.610 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:54.693 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:54.697 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:07:54.699 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:07:54.892 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:07:55.895 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:07:55.898 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:07:56.690 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:07:58.093 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:07:59.791 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:07:59.794 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:01.988 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:08:01.990 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:02.434 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:08:02.789 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:04.891 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:08:04.893 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:08:04.895 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:08:07.390 | TaskManager      | Run task: 'Treat Nodes Stats' on thread[7] / #39984

    2012/07/12-13:08:07.499 | TaskManager      | Run task: 'Purge Event List' on thread[9] / #38128

    2012/07/12-13:08:08.095 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:08:08.098 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:08.192 | TaskManager      | Run task: 'Flush DB' on thread[9] / #38128

    2012/07/12-13:08:08.473 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 29

    2012/07/12-13:08:08.553 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:08:08.825 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:08:08.899 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-13:08:08.922 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:09.996 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:08:10.000 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:10.004 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:08:14.196 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:08:14.199 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:14.574 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:08:14.653 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:08:14.915 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:08:14.989 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:08:14.994 | TaskManager      | Run task: 'Compute Power Links' on thread[9] / #38128

    2012/07/12-13:08:15.012 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:15.094 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:08:15.097 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:08:15.099 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:08:18.291 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:08:20.194 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:08:20.197 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:08:20.300 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:08:20.303 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:20.763 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:08:21.118 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:25.301 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:08:25.305 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:25.308 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:08:26.400 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:08:26.403 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:26.852 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 1950 -> level: 0

    2012/07/12-13:08:26.859 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 1950

    2012/07/12-13:08:27.124 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:08:27.218 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:28.401 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:08:30.394 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:08:30.396 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1365 s

    2012/07/12-13:08:30.398 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1365

    2012/07/12-13:08:32.500 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[7] / #39984

    2012/07/12-13:08:32.503 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:32.952 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-13:08:32.959 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:08:33.223 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:08:33.318 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:33.322 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread[9] / #38128

    2012/07/12-13:08:33.324 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:08:35.011 | TaskManager      | Run task: 'Compute Power Links' on thread[7] / #39984

    2012/07/12-13:08:35.404 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[7] / #39984

    2012/07/12-13:08:35.408 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:35.411 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:08:37.610 | TaskManager      | Run task: 'Purge Event List' on thread[7] / #39984

    2012/07/12-13:08:38.370 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:08:38.374 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 50

    2012/07/12-13:08:38.377 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:08:38.380 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 503

    2012/07/12-13:08:38.383 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 579

    2012/07/12-13:08:38.386 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1417

    2012/07/12-13:08:38.389 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:08:38.393 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342099166

    2012/07/12-13:08:38.511 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:08:38.603 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:08:38.605 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:39.313 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:08:39.407 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:40.511 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:08:40.515 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:44.708 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:08:44.710 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:45.413 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:08:45.507 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:45.610 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:08:45.613 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:48.606 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:08:50.706 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:08:50.710 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:50.813 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:08:50.816 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:51.523 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:08:51.598 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 232

    2012/07/12-13:08:51.620 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:55.112 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:08:55.805 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:08:55.809 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:08:56.912 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:08:56.915 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:08:57.360 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2250

    2012/07/12-13:08:57.696 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 233

    2012/07/12-13:08:57.718 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:08:58.710 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:09:00.911 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:00.915 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1575 s

    2012/07/12-13:09:00.917 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1575

    2012/07/12-13:09:03.010 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:09:03.013 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:03.391 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 29

    2012/07/12-13:09:03.471 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:09:03.826 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:06.022 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:06.026 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:09:06.029 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:09:07.621 | TaskManager      | Run task: 'Purge Event List' on thread:emotion-29: / #6740

    2012/07/12-13:09:07.894 | TaskManager      | Run task: 'Treat Nodes Stats' on thread:emotion-29: / #6740

    2012/07/12-13:09:08.721 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:09:09.120 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:09:09.123 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:09.499 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.PercentLoad' = 30

    2012/07/12-13:09:09.579 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:09:09.926 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:11.118 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:11.122 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:09:11.125 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:09:15.217 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:09:15.223 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:09:15.225 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:15.669 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-13:09:15.676 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:09:15.941 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 231

    2012/07/12-13:09:16.035 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:16.220 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:16.224 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:09:16.227 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:09:18.819 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:09:21.319 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:09:21.320 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:21.322 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:21.323 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:09:21.770 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-13:09:21.777 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:09:22.125 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:26.424 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:26.427 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:09:26.428 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:09:27.420 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:09:27.423 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:27.868 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2160 -> level: 0

    2012/07/12-13:09:27.872 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2160

    2012/07/12-13:09:28.140 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 232

    2012/07/12-13:09:28.234 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:28.917 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:09:31.519 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:31.523 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:09:31.526 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1512

    2012/07/12-13:09:33.419 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getObjectList' on thread:emotion-29: / #6740

    2012/07/12-13:09:33.421 | CN-0K789N-75162-1AE-0045-A06 | Get Object List

    2012/07/12-13:09:35.222 | TaskManager      | Run task: 'Compute Power Links' on thread[10] / #26904

    2012/07/12-13:09:36.526 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[10] / #26904

    2012/07/12-13:09:36.530 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1512 s

    2012/07/12-13:09:37.723 | TaskManager      | Run task: 'Purge Event List' on thread[10] / #26904

    2012/07/12-13:09:38.486 | CN-0K789N-75162-1AE-0045-A06 | !!!!  ERROR : getObjectList: value not defined for UPS.COPIBridge

    2012/07/12-13:09:38.489 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Frequency' = 49.9

    2012/07/12-13:09:38.492 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.ActivePower' = 506

    2012/07/12-13:09:38.493 | CN-0K789N-75162-1AE-0045-A06 | Trig event on System.ApparentPower == 577 -> level: 0

    2012/07/12-13:09:38.497 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.ApparentPower' = 577

    2012/07/12-13:09:38.499 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Frequency' = 49.9

    2012/07/12-13:09:38.501 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.RemainingActivePower' = 1414

    2012/07/12-13:09:38.503 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerSummary.RunTimeToEmpty == 2220 -> level: 0

    2012/07/12-13:09:38.509 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:09:38.511 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.Time' = 1342099227

    2012/07/12-13:09:38.514 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread[9] / #38128

    2012/07/12-13:09:38.516 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:38.929 | TaskManager      | Run task: 'Flush DB' on thread[7] / #39984

    2012/07/12-13:09:39.228 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 233

    2012/07/12-13:09:39.302 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 234

    2012/07/12-13:09:39.326 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:41.625 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:41.629 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:09:41.632 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:09:44.524 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:09:44.527 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:45.321 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:46.725 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:46.729 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:09:49.032 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:09:50.625 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:09:50.627 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:51.076 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:09:51.431 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:51.825 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:09:51.829 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:09:51.832 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1533

    2012/07/12-13:09:55.334 | TaskManager      | Run task: 'Compute Power Links' on thread:emotion-29: / #6740

    2012/07/12-13:09:56.727 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:09:56.730 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:09:56.931 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread[9] / #38128

    2012/07/12-13:09:56.934 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1533 s

    2012/07/12-13:09:57.174 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2220

    2012/07/12-13:09:57.436 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Input[1].Voltage == 234 -> level: 0

    2012/07/12-13:09:57.442 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Input[1].Voltage' = 234

    2012/07/12-13:09:57.511 | CN-0K789N-75162-1AE-0045-A06 | Trig event on UPS.PowerConverter.Output.Voltage == 235 -> level: 0

    2012/07/12-13:09:57.517 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerConverter.Output.Voltage' = 235

    2012/07/12-13:09:57.539 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:09:59.132 | TaskManager      | Run task: 'Flush DB' on thread:emotion-29: / #6740

    2012/07/12-13:10:02.027 | TaskManager      | Run task: 'Check Shutdown Criteria' on thread:emotion-29: / #6740

    2012/07/12-13:10:02.031 | ShutdownManager  | checkShutdownCriteria: CN-0K789N-75162-1AE-0045-A06/#1 / shutdownInProgress -> false / 'remainingCapacityLimitDate' -> 1554 s

    2012/07/12-13:10:02.033 | CN-0K789N-75162-1AE-0045-A06 | Set 'System.EstimatedRunTimeToShutdown' = 1554

    2012/07/12-13:10:02.826 | TaskManager      | Run task: '[CN-0K789N-75162-1AE-0045-A06] -> getSummary' on thread:emotion-29: / #6740

    2012/07/12-13:10:02.828 | CN-0K789N-75162-1AE-0045-A06 | Get Summary

    2012/07/12-13:10:03.274 | CN-0K789N-75162-1AE-0045-A06 | Set 'UPS.PowerSummary.RunTimeToEmpty' = 2190

    2012/07/12-13:10:03.621 | CN-0K789N-75162-1AE-0045-A06 | Set System.CommunicationLost = 0

    2012/07/12-13:10:04.309 | NodeManager      | Close driver for 'CN-0K789N-75162-1AE-0045-A06' of class 'ups_pdc'

    2012/07/12-13:10:04.311 | NodeManager      | Close driver for '192.168.19.199' of class 'nmc'

  • 1393

    0

    Posted July 16th, 2012 04:00

    Hi There, is there a way you can get me the entire log file as an attachment?  Maybe upload to an online share and post the link?