Datacenter Capacity Planner power/cooling numbers

I have been tasked with computing the cooling requirements for new server rooms and have been trying to use the Datacenter Capacity Planner tool to accomplish this.

I am confused by the results for Power (wattage and cooling). I am configuring racks of 1750's, 1850's, 2650's, 2850's, and 2950's. The wattage and cooling numbers come back the same if I configure them with redundant or non-redundant power supplies. I don't see how that can be accurate.

For example: a PE2650 shows thermal watts usage of 357W and a need of 0.1 tons sensible cooling whether it is configured as a single or dual power supply unit. Is that for one or two power supplies? Also, is it possible to get the plain BTU generation instead of the sensible cooling suggestion?

Thank you

180 Posts

January 13th, 2010 11:00

CPatrickB-

I have forwarded your concerns to the data center infrastructure team for clarification. A response is forthcoming.

KongY

2 Posts

January 13th, 2010 12:00

I spoke to a Dell rep via chat and got the following numbers in case any one else is looking for them (I had a devil of a time finding them online).

All numbers are dual power-supply configurations
PE1750: 2052 BTU
PE1850: 2130 BTU
PE2650: 1415 BTU
PE2850: 2388 BTU
PE2950: 2697 BTU

Hope this helps anyone else looking for these elusive numbers!

1 Message

January 14th, 2010 10:00

What you'll find is that this tool was created way after some of the products you mention. The second number in each name (the "9" in 2950) is it's generation number, the 9 being the 9th generation. With this later hardware, there is accompanying power supply efficiency information associated with it. The logic would suggest that with a redundant configuration, the load is being shared between 2 supplies, they are loaded half as much, and are operating at an efficiency that is lower due to the lower utilization. The older servers do not carry the efficiency variation within their data attributes. There is a single number efficiency associated with them, so whether they are heavy loaded (non-redudant) or light loaded, the tool thinks they are the same efficiency. Sorry, but we just lacked the data at the time the tool was built.

To get BTUs, you can change to metric by clicking the "properties" button. It's going to also change to degC, kg, and cu.m/hr