PowerEdge 2900: REDUNDANT POWER SUPPLY connection?

Hello, we have four Power Edge 2900 servers (each with a couple of redundant power supplies). What's the best way to connect them to the UPS?

Right now we have all the eight cables connected to one APC RT3000.

Is it better to connect 4 cables to one UPS and the remaining 4 cables to another UPS? I mean every server connected to 2 UPS at the same time.

Thank you

847 Posts

January 17th, 2012 09:00

Or go old school?  4 to the UPS and 4 to the wall.   That is how we used to do it back in the day.

3 Apprentice

 • 

944 Posts

January 17th, 2012 09:00

correct, 4 to one ups, 4 to another ups, and each ups should be on its own electrical grid/breaker. redundancy is the name of the game here. the two UPS should not be on the same circuit breaker andif possible, the UPS should be on completely different electrical power sources in your building, so if one goes, the other will stay up. same for  your switches etc. Its really a matter of how critical it is for your systems and switches/network to stay up.

Moderator

 • 

8.8K Posts

January 17th, 2012 09:00

ItalP,

The best practice isn't to have the power supplies going to individual UPS's. Best practice is to have them running to the same UPS, but to have the UPS connected to separate circuits. You can have them split to 2 different UPS's it adds another level of redundancy.

2 Posts

January 18th, 2012 00:00

First of all, thank you everybody for the replies.

Is it possible to connect the power supplies to different models of UPS? I mean, 4 to the APC RT3000 and 4 to a APC SMT2200I? Or it's better to use the same model?

4 Operator

 • 

9.3K Posts

January 18th, 2012 06:00

Using 2 different models or 2 identical models of different production dates (at least a few months apart) makes it less likely that a problem with the design/firmware or the battery ages causes downtime on both UPSes at the same time.

3 Apprentice

 • 

944 Posts

January 18th, 2012 07:00

be sure to test the configuration to see how long it takes for the UPS to pickup the load in case of a power loss. There are cases where some system power supplies dont like the power coming from a UPS because of the wave form and amplitude that the UPS is putting out when a power outage occurs. Some UPS have enough of a delay to actually provide power to the system, that the power supply thinks it lost power.