Server Administrator Instrumentation Service Event ID: 1403

The following system event warning is being displayed:
 
Event Type: Warning
Event Source: Server Administrator
Event Category: Instrumentation Service
Event ID: 1403
Date:  9/4/2006
Time:  11:32:20 AM
User:  N/A
Computer: TLTSVR-CHARVAX
Description:
Memory device status is non-critical
Memory device location: DIMM1_B
Memory device status is non-critical
Single bit warning error rate exceeded
 
Any comment?

Message Edited by TLTITSDept on 09-05-200601:34 PM

2 Intern

 • 

827 Posts

September 6th, 2006 13:00

This is a simple SBE (single bit error) on your DIMM.  The ECC of the DIMM is fixing the error and Server Administrator is letting you know.  Simple troubleshooting steps:

Swap Dimm 1A and 1B
Boot back into OS and use SA to clear the hardware log
Watch for new errors

If the error return and follow the DIMM then have it replaced.  If it stays with the same slot then you may have a MB problem.

2 Posts

September 7th, 2006 14:00

Thanks,

This advise was applied.  Dell has issued replace memory after a testing revealed problems in one DIMM.