This post is more than 5 years old

1 Rookie

 • 

34 Posts

65471

September 19th, 2016 02:00

Loud fan noise

Hello, 

I am prepairing new Dell t430 server with two cpu utins. When srever starts fan noise is normal, but when I plug in PCIe Intell P3500 nvme ssd fans ramp up and is very loud. All frimware and bios are upgraded to the most recent ones. How to reduce fan speed?

1 Rookie

 • 

34 Posts

December 11th, 2016 22:00

Problem was solved with lifecycle controler update 2.40.40. All fans behave normaly now.

1 Rookie

 • 

34 Posts

September 19th, 2016 23:00

I have  Intel 750 ssd and if I put it in server works normaly.

1 Rookie

 • 

34 Posts

September 19th, 2016 23:00

I ran these commands:

ipmitool.exe -I lanplus -U root -P calvin -H 192.168.192.168 raw 0x30 0x30 0x01 0x00

ipmitool.exe -I lanplus -U root -P calvin -H 192.168.192.168 raw 0x30 0x30 0x02 0xff 0x46

But I get error:

Error: Unable to establish IPMI v2 / RMCP+ session
Unable to send RAW command (channel=0x0 netfn=0x30 lun=0x0 cmd=0x30)

1 Rookie

 • 

34 Posts

September 20th, 2016 01:00

I managed to run these commands but nothing has changed, fans still run at 85%. Maybe I am using bad raw command if so can you give me correct one?

1 Rookie

 • 

34 Posts

September 21st, 2016 01:00

Command that you gave did not solve the problem, system fan still runs at 85% speed. Syestem uses 4 ram slots(4x16GB), 2 cpu slots, 2 hdd slots, 2 pcie slots.

1 Rookie

 • 

34 Posts

September 21st, 2016 10:00

I have bmc  utility instaled on my windows machine. I  can connect  to  server. I used thread  to check status

"and here is the command to check the status.

raw 0x30 0xce 0x01 0x16 0x05 0x00 0x00 0x00"


I  get 16 05 00 00 00 05 00 01 00 00

1 Rookie

 • 

34 Posts

September 22nd, 2016 01:00

I spotted one thing. When i run bmc comand

ipmitool -I lanplus -H 192.168.192.168 -U root -P calvin raw 0x30 0xce 0x00 0x16 0x05 0x00 0x00 0x00 0x05 0x00 0x01 0x00 0x00

On iDrac I can see that fan rmp changed from 10080 to 4200, but fans spin at the same speed (85%). Is that raw command universal, if no then maybe I need another command?

1 Rookie

 • 

34 Posts

September 22nd, 2016 09:00

Fan noise, nor speed have not changed,  just numbers that  idrac shows are lower. I applied bios 2.2.5  and  idrac 2.30.30 updates. Maybe I have faulty fan or motherboard? Temps are max 42 C.

1 Rookie

 • 

34 Posts

September 22nd, 2016 23:00

But why it behaves normaly with pcie Intel 750 SSD. I do not think that fan is faulty.

1 Rookie

 • 

34 Posts

September 24th, 2016 11:00

I  tried new fan,  still same happens

2 Intern

 • 

63 Posts

September 26th, 2016 14:00

Hi,

I happen to have a T430 with quite a few non-Dell PCI-E cards:

- an NVidia K600 GPU)

- a dual-8Gbps Qlogic FC Card

- an Intel Quad e1000e.

- I have 12 Dimms and 2 x 85W cpus.

My fan speed is usually around 1440 rpm. I followed the same instructions as you did.

Here are my readings:

# ipmitool raw 0x30 0xce 0x01 0x16 0x05 0x00 0x00 0x00
16 05 00 00 00 05 00 01 00 00

and:

# ipmitool sdr list full
Inlet Temp | 22 degrees C | ok
Fan1 | 1440 RPM | ok
Fan2 | disabled | ns
Current 1 | 0.40 Amps | ok
Current 2 | no reading | ns
Voltage 1 | 116 Volts | ok
Voltage 2 | no reading | ns
Pwr Consumption | 182 Watts | ok
Temp | 51 degrees C | ok
Temp | 48 degrees C | ok
CPU Usage | 35 percent | ok
IO Usage | 0 percent | ok
MEM Usage | 0 percent | ok
SYS Usage | 34 percent | ok

I wonder what could be different in your system to make it so loud..

Good luck,

Vincent

1 Rookie

 • 

34 Posts

September 27th, 2016 00:00

I tried what you suggested, but fan is still spinning at the same speed 

1 Rookie

 • 

34 Posts

September 28th, 2016 00:00

C:\Program Files (x86)\Dell\SysMgt\bmc>racadm -r 192.168.192.168 -u root -p calvin getsensorinfo
Security Alert: Certificate is invalid - Certificate is not signed by Trusted Third Party
Continuing execution. Use -S option for racadm to stop execution on certificate-related errors.

SEC0701: Warning: Default username and password are currently in use.
It is strongly recommended to change the default password immediately.

To change the password, run the following racadm command:
"racadm set iDRAC.Users. .Password ".

Alternatively, to avoid this warning message run the following racadm command:
"racadm set iDRAC.Tuning.DefaultCredentialWarning Disabled".


Sensor Type : POWER
                                   
PS1 Status                      Present                  AC
PS2 Status                      Present                  AC

Sensor Type : TEMPERATURE
                  [R/W]  [R/W]
[Key = iDRAC.Embedded.1#SystemBoardInletTemp]
System Board Inlet Temp       Ok      20C      -7C  47C      3C       42C

[Key = iDRAC.Embedded.1#CPU1Temp]
CPU1 Temp                     Ok      32C      3C   87C      8C       82C

[Key = iDRAC.Embedded.1#CPU2Temp]
CPU2 Temp                     Ok      31C      3C   87C      8C       82C



Sensor Type : FAN
                                         
System Board Fan1               Ok          4200RPM     240RPM      NA          85%

Sensor Type : VOLTAGE
                                 
CPU1 M01 VTT PG                 Ok          Good                NA          NA
CPU1 M23 VTT PG                 Ok          Good                NA          NA
CPU1 M23 VDDQ PG                Ok          Good                NA          NA
System Board 3.3V PG            Ok          Good                NA          NA
System Board VCCIO PG           Ok          Good                NA          NA
System Board 5V AUX PG          Ok          Good                NA          NA
CPU2 M01 VDDQ PG                Ok          Good                NA          NA
CPU2 M01 VTT PG                 Ok          Good                NA          NA
CPU2 M23 VDDQ PG                Ok          Good                NA          NA
CPU1 M01 VDDQ PG                Ok          Good                NA          NA
CPU2 M01 VPP PG                 Ok          Good                NA          NA
CPU1 M01 VPP PG                 Ok          Good                NA          NA
CPU1 5V SWITCH PG               Ok          Good                NA          NA
CPU2 M23 VPP PG                 Ok          Good                NA          NA
CPU1 VCORE PG                   Ok          Good                NA          NA
CPU2 VCORE PG                   Ok          Good                NA          NA
CPU1 M23 VPP PG                 Ok          Good                NA          NA
CPU2 M23 VTT PG                 Ok          Good                NA          NA
System Board 1.05V PG           Ok          Good                NA          NA
System Board 2.5V AUX PG        Ok          Good                NA          NA
System Board 1.5V AUX PG        Ok          Good                NA          NA
CPU1 FIVR PG                    Ok          Good                NA          NA
CPU2 FIVR PG                    Ok          Good                NA          NA
System Board 1.5V PG            Ok          Good                NA          NA
System Board PS1 PG Fail        Ok          Good                NA          NA
System Board PS2 PG Fail        Ok          Good                NA          NA
System Board DIMM PG            Ok          Good                NA          NA
PS2 Voltage 2                   Ok          210.00V             NA          NA
System Board BP1 5V PG          Ok          Good                NA          NA
PS1 Voltage 1                   Ok          210.00V             NA          NA

Sensor Type : CURRENT
                  [R/W]  [R/W]
[Key = iDRAC.Embedded.1#PS2Current2]
PS2 Current 2                 Ok      0.0Amps  NA   NA       0Amps       0Amps

[Key = iDRAC.Embedded.1#SystemBoardPwrConsumption]
System Board Pwr Consumption  Ok      84Watts  NA   1974Watts 0Watts       1792Watts

[Key = iDRAC.Embedded.1#PS1Current1]
PS1 Current 1                 Ok      0.0Amps  NA   NA       0Amps       0Amps


Sensor Type : PROCESSOR
                                           
CPU1 Status                     Ok          Presence_Detected   NA          NA
CPU2 Status                     Ok          Presence_Detected   NA          NA

Sensor Type : MEMORY
                                           
DIMM A1                         Ok          Presence_Detected   NA          NA
DIMM A2                         Ok          Presence_Detected   NA          NA
DIMM A3                         N/A         Absent              NA          NA
DIMM A4                         N/A         Absent              NA          NA
DIMM A5                         N/A         Absent              NA          NA
DIMM A6                         N/A         Absent              NA          NA
DIMM A7                         N/A         Absent              NA          NA
DIMM A8                         N/A         Absent              NA          NA
DIMM B1                         Ok          Presence_Detected   NA          NA
DIMM B2                         Ok          Presence_Detected   NA          NA
DIMM B3                         N/A         Absent              NA          NA
DIMM B4                         N/A         Absent              NA          NA

Sensor Type : BATTERY
                                 
System Board CMOS Battery       Ok          Present             NA          NA

Sensor Type : PERFORMANCE
                                    
System Board Power Optimized    Ok          Not Degraded   NA        NA

Sensor Type : INTRUSION
                      
System Board Intrusion          Closed         Power ON

Sensor Type : REDUNDANCY
                                   
System Board PS Redundancy      Disabled                 PSU
System Board Fan Redundancy     Disabled                 Fan

Sensor Type : SYSTEM PERFORMANCE
                  [R/W]  [R/W]
[Key = iDRAC.Embedded.1#SystemBoardCPUUsage]
System Board CPU Usage   Ok             0%      NA  NA    NA        101%

[Key = iDRAC.Embedded.1#SystemBoardIOUsage]
System Board IO Usage    Ok             0%      NA  NA    NA        101%

[Key = iDRAC.Embedded.1#SystemBoardMEMUsage]
System Board MEM Usage   Ok             0%      NA  NA    NA        101%

[Key = iDRAC.Embedded.1#SystemBoardSYSUsage]
System Board SYS Usage   Ok             0%      NA  NA    NA        101%

1 Rookie

 • 

34 Posts

September 28th, 2016 00:00

C:\Program Files (x86)\Dell\SysMgt\bmc>ipmitool -I lanplus -H 192.168.192.168 -U root -P calvin sdr list full
Inlet Temp       | 21 degrees C      | ok
Fan1             | 4200 RPM          | ok
Fan2             | disabled          | ns
Current 1        | 0.05 Amps         | ok
Current 2        | 0.05 Amps         | ok
Voltage 1        | 220 Volts         | ok
Voltage 2        | 220 Volts         | ok
Pwr Consumption  | 84 Watts          | ok
Temp             | 31 degrees C      | ok
Temp             | 32 degrees C      | ok
CPU Usage        | 0 percent         | ok
IO Usage         | 0 percent         | ok
MEM Usage        | 0 percent         | ok
SYS Usage        | 0 percent         | ok

1 Rookie

 • 

34 Posts

September 28th, 2016 00:00

C:\Program Files (x86)\Dell\SysMgt\bmc>racadm -r 192.168.192.168 -u root -p calvin get system.thermalsettings

[Key=system.Embedded.1#ThermalSettings.1]
#FanSpeedHighOffsetVal=55
#FanSpeedLowOffsetVal=20
#FanSpeedMaxOffsetVal=100
#FanSpeedMediumOffsetVal=35
FanSpeedOffset=Low Fan Speed
#MFSMaximumLimit=100
#MFSMinimumLimit=85
MinimumFanSpeed=255
ThermalProfile=Default Thermal Profile Settings
ThirdPartyPCIFanResponse=Disabled

No Events found!