I have noticed that PowerEdge servers have a hidden setting for liquid cooling. After accidentally enabling it on a first boot of a system. I would like to know if it's possible to disable? I've seen some documentation and I can see it's readable from RACADM under System.ThermalConfig.LiquidCoolSetting however it is read only? Is this by design as I have a server overheating due to the fans not ramping up enough. I can cool the system only by using a fan offset.
@DELL-Charles R is this possible to do without an engineer and without support? I would just like a simple quick way to do it. Even a point in the correct direction if possible.
Sure you could try it with the manual if you be careful and skilled enough you could do this by yourself if you're not sure I would recommend to involve an engineer.
with kind regards Martin/ Liebe Grüße Martin
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!
@Dell-Martin S hi, could you possibly point out where this would be in the manual? I'm confident on working with these systems but cannot find where I would be able to find the procedure. All I could figure is there's a way to reset the board to detect a new chassis causing it to ask for water cooling to be enabled again? I wouldn't know how to trigger that new chassis detection however. All I can find is the read-only config value in the system attributes.
@Dell-Martin S I've already done the physical side of things. I have replaced the liquid cooling modules with high performance air cooled heatsinks. My issue is the software side, this value is still set to enabled with no way to disable it. I believe this is causing my overheating issues as the fans are not ramping up enough.
For example Dell PowerEdge R760 liquid cooling relies on a Direct Liquid Cooling (DLC) module that is automatically managed by the server and its integrated software; there are no manual user settings for the cooling loop itself, but rather performance is dependent on the system's configuration, such as processor TDP and installed heat sinks. The system uses sensors to detect pressure drops and alerts the user to potential leaks.
with kind regards Martin/ Liebe Grüße Martin
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!
@Dell-Martin S interesting, I have 3 systems. 2 have this liquid cool setting disabled and do not overheat, the one with this enabled is overheating. I have swapped CPUs and the only thing I can narrow it down to is this setting. Which was set when this was displayed by the system which I stupidly pressed Y to on one system. What I know is this changed the setting under System.ThermalConfig.LiquidCoolSetting from Unknown to Enabled.
DELL-Charles R
Moderator
•
4730 Posts
•
25476 Points
3
1
Posted September 29th, 2025 13:21
Hello,
Did you try the steps in the KB article Martin posted?
It is the same steps in the internal documentation I found.
The ThermalConfig setting can be corrected through an undocumented OEM IPMI command.
#Set to Air Cooled
ipmitool raw 0x30 0xD0 0x0 0x38 0x37 0x0 0x0 0x0 0x37 0x0 0x73 0x79 0x73 0x74 0x65 0x6d 0x2e 0x65 0x6d 0x62 0x65 0x64 0x64 0x65 0x64 0x2e 0x31 0x23 0x74 0x68 0x65 0x72 0x6d 0x61 0x6c 0x63 0x6f 0x6e 0x66 0x69 0x67 0x2e 0x31 0x23 0x6c 0x69 0x71 0x75 0x69 0x64 0x63 0x6f 0x6f 0x6c 0x73 0x65 0x74 0x74 0x69 0x6e 0x67 0x3d 0x30
The response data should be:
38 37 00 00 00
Note: IPMITOOL requires root/admin privileges when run from within the host operating system.
Reboot the iDRAC (ipmitool mc reset cold) and reboot the host operating system (reboot) to allow the correct thermal table to reload.
https://www.dell.com/support/kbdoc/en-us/000319232/poweredge-17g-servers-prompting-for-liquid-cool-settings-input-during-post-after-idrac10-update
DELL-Charles R
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Accept as Solution’. ‘Thumbs up’ the posts you like!