The table below is taken from an actual cab. I have gone onto each DRAC and recorded the information below. My issue is that some of my PDUs are exceeding their ratings but only on one side. Why do some of the servers pull 0.2A more on one PSU than the other and why is it normally PS1?
The servers are a mixture of 13G and 14G but both are affected equally
After Hot Spare is enabled, PSUs can become active or go to sleep based on load. If Hot Spare is enabled, asymmetric electrical current sharing between the two PSUs is enabled. One PSU is awake and provides the majority of the current; the other PSU is in sleep mode and provides a small amount of the current. This is often called 1 + 0 with two PSUs and hot spare enabled.
DELL-Charles R
Social Media and Communities Professional Dell Technologies | Enterprise Support Services #IWork4Dell
Did I answer your query? Please click on ‘Accept as Solution’. ‘Thumbs up’ the posts you like!
I understand the hot spare rule but as you can see most of my servers do not have hot spare enabled and there is still a small mismatch between PS1 and PS2. 0.2A is not a great deal per server but balancing the load between PS1 and PS2 might allow me to fit in another server in the rack without exceeding my power budget
Hello, as far as I know amperage does not need to match however PSUs have to supply enough amperages as required. Unfortunately, I don't have much detailed information to add other than what Charles said. I found a doc for PSU missmatch behavior for 12G. It's useful for generic information. https://dell.to/3yfV28k
DELL-Erman O
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!
DELL-Charles R
Moderator
•
4730 Posts
•
25476 Points
564
0
Posted July 6th, 2022 13:00
Hello Jaimie,
This should help. iDRAC user guide: Page 169
https://dell.to/3uuApo0
After Hot Spare is enabled, PSUs can become active or go to sleep based on load. If Hot Spare is enabled, asymmetric electrical current sharing between the two PSUs is enabled. One PSU is awake and provides the majority of the current; the other PSU is in sleep mode and provides a small amount of the current. This is often called 1 + 0 with two PSUs and hot spare enabled.
DELL-Charles R
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Accept as Solution’. ‘Thumbs up’ the posts you like!