It sounds like you lost the second power supply grid. If one power grid fails, three power supplies lose their AC source, and the three power supplies on the other grid remain powered, providing sufficient power for the system to continue running. Now with you stating that the power supplies aren't showing a "Power Present" green light, it doesn't sound like an issue with the midplane, but possibly an issue with the source power. A couple ways to test this would be to place known good power supplies, as well as cables, in the failed power supply slots. Then instead of plugging the known good cables into your UPS/APC/PDU run them to a known good power source. Then see if it shows the green power present light. Another way to test the slots specifically would be to power down the enclosure and then move the 1,2, and 3 power supplies, with their existing working cables, over to the 4,5, and 6 slots.
Let me know what you see.
DELL-Chris H
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!
The grid isn't a part, it is the separation of the power supplies into redundant groups. When you use AC redundancy mode you would want to provide power to each grid (Grid 1= PS1,2, and 3 & Grid 2= 4,5, and 6) from separate sources, This will also increase the actual redundancy of the power supplied to the servers.
DELL-Chris H
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!
That is the way it was setup and all of a sudden power supplies 4,5, and 6 are reporting failed. even when i replace them with what i thought were good ones i had on hand. Once I get the brand new ones i'l try them.
What i was trying to explain was if its not the power supplies what part would need replacing.
when did technicians stop using DVMs or oscilloscopes? To see if you've lost AC on a Grid, measure the power coming out the power cord just before you plug it into the power supply.
DELL-Chris H
7 Practitioner
•
9682 Posts
•
48046 Points
1501
0
Posted August 10th, 2015 09:00
SummerSF,
It sounds like you lost the second power supply grid. If one power grid fails, three power supplies lose their AC source, and the three power supplies on the other grid remain powered, providing sufficient power for the system to continue running. Now with you stating that the power supplies aren't showing a "Power Present" green light, it doesn't sound like an issue with the midplane, but possibly an issue with the source power. A couple ways to test this would be to place known good power supplies, as well as cables, in the failed power supply slots. Then instead of plugging the known good cables into your UPS/APC/PDU run them to a known good power source. Then see if it shows the green power present light. Another way to test the slots specifically would be to power down the enclosure and then move the 1,2, and 3 power supplies, with their existing working cables, over to the 4,5, and 6 slots.
Let me know what you see.
DELL-Chris H
Social Media and Communities Professional
Dell Technologies | Enterprise Support Services
#IWork4Dell
Did I answer your query? Please click on ‘Mark as Accepted Answer’. ‘Thumbs up’ the posts you like!