Unsolved

This post is more than 5 years old

6 Posts

11209

January 18th, 2008 12:00

Data Center Capacity planner-tool

Couple of questions about DDCP. What's the Flow Rate (CFM) at the report. (For PE2950 this is 93,40.) In the report theres a column Thermal (watts) displayed for individual devices and in the summary the sum of this columns values are as BTU/h. What's BTU/h? Also how to find out the heating capacity of a server or is BTU a thermal unit? If so what is the actual Total power consumption of the rack? Anyway, this is a useful tool. I just need to understand the results... Thanks

6 Operator

 • 

9.3K Posts

January 18th, 2008 14:00

Have you checked Google or Wikipedia for a definition of BTU?

The flowrate is the amount of air that's blown out of the fans in a certain period of time.

6 Posts

January 21st, 2008 03:00

OK. Do you know what's the unit "CFM" of the airflow? Best bet for BTU I found was British Thermal Unit. I'm not familiar with this stuff so perhaps I need to do some more searching... Thanks.

2 Intern

 • 

287 Posts

January 24th, 2008 12:00

12,000 per ton of air.
 
With around 600 cfm coming out of your tile, life in the datacenter should be good.
 
An easy rule (without having to really learn) would be 20,000-30,000 tons per 1000 sqaure feet in a raised floor center.

1 Rookie

 • 

11 Posts

July 9th, 2009 12:00

I beileve the author meant 20,000-30,000 BTU.  2 tons of A/C is 24,000 BTU and 3 tons would be 36,000 BTU.  That is likely a bit low.  A single Dell rack about 1/2 full of say 2950 III servers rates at consuming over a ton of A/C.

Since the electricity consumed by the equipment directly correlates to heat output, you will typically need about 1 ton of A/C for every 3500-4000 watts of electricity you consume.

0 events found

No Events found!

Top