Couple of questions about DDCP. What's the Flow Rate (CFM) at the report. (For PE2950 this is 93,40.) In the report theres a column Thermal (watts) displayed for individual devices and in the summary the sum of this columns values are as BTU/h. What's BTU/h? Also how to find out the heating capacity of a server or is BTU a thermal unit? If so what is the actual Total power consumption of the rack? Anyway, this is a useful tool. I just need to understand the results... Thanks
0 events found
No Events found!


Dev Mgr
6 Operator
•
9.3K Posts
0
January 18th, 2008 14:00
The flowrate is the amount of air that's blown out of the fans in a certain period of time.
Bob Cat
6 Posts
0
January 21st, 2008 03:00
AEV
2 Intern
•
287 Posts
0
January 24th, 2008 12:00
Corey.McCormick
1 Rookie
•
11 Posts
0
July 9th, 2009 12:00
I beileve the author meant 20,000-30,000 BTU. 2 tons of A/C is 24,000 BTU and 3 tons would be 36,000 BTU. That is likely a bit low. A single Dell rack about 1/2 full of say 2950 III servers rates at consuming over a ton of A/C.
Since the electricity consumed by the equipment directly correlates to heat output, you will typically need about 1 ton of A/C for every 3500-4000 watts of electricity you consume.