Power supply wattage and UPS question
I'm trying to decide what rackable UPS to buy.
So I have a Poweredge 2850 with redundant power supplies. It says the power supply is rated at 700W. Does this mean because I have redundant power my server is actually drawing 1400W while in use?
If so, what kind of UPS should I get? Does this mean I need a 1430W / 2200VA UPS? If I got a 480W UPS is that too small? How do I know? I'll have a small switch and a firewall on it too.
Thanks.
No Events found!



DELL-Charles R
Moderator
•
4.6K Posts
0
April 2nd, 2025 17:31
Hello,
As you are aware this is a dated system.
I'm unable to find much information on it.
I have the hardware manual here but it does not list the PSU specs:
https://dl.dell.com/content/docu5165_CX700%20Storage%20Processor%20Enclosure%20Hardware%20Reference.pdf?language=en_us
I did find this posting with the PSU label
https://www.ebay.com/itm/404680464523?_skw=Original+Dell+EMC+Clarion+CX700+Power+Supply+118031924+XPE+9T607&itmmeta=01JQVR30839MY35H334PFJ4BHN&hash=item5e38d5d88b:g:bBYAAOSwMPxleh6k
Other than those I don't have any more information on the CX7200
Ferb
23 Posts
0
January 6th, 2006 19:00
http://www.dell.com/downloads/global/corporate/environ/PE_2850.pdf
The dual power supplies can each provide up to 700W, but this will never be met. And even though you have two power supplies, the 393W load is just going to be balanced between the two.
Following APC's little tool, it looks like a SmartUPS XL 1400VA would be great. They're pricier than the non-XL series, but allow you do daisy-chain battery packs for more runtime if you need it in the future. This is assuming you're using 120V mains. If you're using 208V, there are other 208V rackable power supplies too.
The 480W UPS would likely be right on the bleeding edge of power, thus minimizing the amount of backup power time available.
ferb!
speedstep
9 Legend
•
47K Posts
0
January 11th, 2006 03:00
Go with at least a 2500VA unit. REMEMBER THAT VA is not EQUAL TO WATTS.
What is the difference between a volt-amp (VA) and a Watt?
Equipment I have seen (such as computer backup power supplies)
have 2 different numbers for this rating. The watt rating is
typically 65% of the VA rating. So a 1000VA UPS is Actually 650 watts.
500VA UPS is 325 WATTS.
Ferb
23 Posts
0
January 12th, 2006 15:00
The volt-amp rating on a back up supply shows how "bad" the load can get in terms of max current and max voltage. Power supplies with active power factor correction (PFC) are somewhere in the neighbourhood of 3% more VA than Watts. But an old style supply may be closer to 30-40%.
ferb!
jameskuder70
1 Rookie
•
2 Posts
0
April 2nd, 2025 15:16
How do I find the wattage for the following as I look for a UPS
DELL_R660.2x16i_2.5GHz.64Gb_AC
CX7200A Server
DELL-Charles R
Moderator
•
4.6K Posts
0
April 2nd, 2025 15:28
Hello,
Here you can find PSU specifications for R660
Page 29
http://del.ly/61216FZqHw
jameskuder70
1 Rookie
•
2 Posts
0
April 2nd, 2025 16:28
@DELL-Charles R What about the CX7200 Server?