Need Assistance with specing a Rack Solution
Hi,
I have a situation with 14 - Power Edge 2950 III with redundant power supplies that will be fully loaded spread across two Dell 4210 racks and need some direction or help with a sizing a UPS and proper PDU setup. Based on example calcs from Racksolutions here is what I have so far:
2950 III
750W
750 + 20% = 900W
750 - 20% = 600W
900W/120VAC = 7.5A (max)
750W/120VAC = 6.25A (spec)
600W/120VAC = 5A (min)
6 Servers on 1 PDU
7.5A * 6 servers = 45A (Max Load)
6.25A * 7 servers = 43.75A (spec)
5A * 9 Servers = 45A (min)
I would like to use a fully manageable PDU like the APC switched PDUs and I forgot to include a monitor /keyboard,
1 -48 port gig switch, KVM solution (Dell), a rack fan for each rack and wiggle room for growth.
Thank you,
-cityh-
BTW - How accurate is the Dell Datacenter Sizing tool - the numbers seem off to me.