WS-MAN Connection Issue

I am trying to add a chassis per the instruction with WS-MAN.  I am getting the following error:

Failed to Add
Device communication failed. Check the network connectivity or protocol credentials. subordinate error code : 0x8f011001 [0x8E040201]

I know that WS-MAN works because I have used the Dell Troubleshooting Tool and it returns the correct information.  It also works in OME.

I have tried checking/unchecking WS-MAN Validate Certificate check box and get the same result.

Any suggestions on how to resolve?  Thanks!  

November 15th, 2012 12:00

My suggestion would be to uncheck the "Validate Certificate" box so Power Center doesn't do any checking, delete the chassis from devices, and then do a re-discovery.  Simple test I'd do for connectivity is to open a browser on the server running Power Center and verify that you can login to the CMC from there - https://m1000e, root, password.  Sometimes when using the troubleshooting tool in the past I've forgotten that it needs to be run on the server and not on the laptop that I use to access the server.

1 Rookie

 • 

18 Posts

November 15th, 2012 21:00

Hi Roger, looks like this particular issue was due to the CMC version.  OMPC only works on CMC 3.x or higher.  Thanks!!